Ask Experts Questions for FREE Help !
Ask
    Runcis's Avatar
    Runcis Posts: 1, Reputation: 1
    New Member
     
    #1

    Sep 11, 2007, 07:49 PM
    Testing Dual Pole 50x2 GFI Breaker
    I have a dual pole screw-in Cuttler Hammer breaker with ground fault interrupter, the connected poles have 50 amps each. The breaker is used to connect to a hot tub. I'd like to know if the breaker is okay.

    I've tested and found current on the IN side, with none on OUT, with the switch firmly on. The GFI doesn't work, that is, when pressed it doesn't return. I've unplugged the easy stuff in the hot tub (i.e. pumps, lights). The heater is hard wired. I had trouble with the GFI on the breaker before and stopped testing it for fear that I wouldn't be able to reset it. I had to remove the pump, so I shut off the breaker. Now the breaker doesn't work at all.

    Thanks for your help.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Sep 11, 2007, 08:26 PM
    Cut the main power in the panel. Remove the two outgoing wires on the breaker. Restore power. See if the breaker will stay in the on position with nothing connected. If it stays on you have a real ground fault.

    You cannot hold a breaker "ON" because of the way it's designed.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Sep 12, 2007, 04:36 PM
    You stopped testing the breaker because you feared you could not reset it?

    I am glad I was not visiting and sitting in your tub with malfunctioning GFI breaker.

    Time for a new breaker, and per the manufacturers instructions , all GFI devices must be tested monthly.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

30 Amp Double Pole Breaker is hot and tripping [ 10 Answers ]

Hi, I just got a Maytag Neptune Dryer a week ago. I have it plugged in to our old dryer outlet (which was replaced less than a year ago) which is 3 prong. The dryer voltage is 240 volts and I am running it on a 30 amp double pole breaker. The problem is, this is new electrical wiring and a...

Using a Double Pole Breaker to feed two circuits [ 11 Answers ]

I have 40' run from the main panel with BX and want to use 14/3 instead of two runs of 14/2. Is there a problem using a double pole breaker (15amp) to feed (with 14/3) a split receptacle and then a lighting circuit on one half and 4 receptacles on the other? Is the only drawback is when one...

Two Single Pole GFI's = one Double Pole 220v GFI? [ 6 Answers ]

Hello there, Installing a pool motor, 220v hayward northstar two speed. Could not find a double pole 40 amp GFI, electric supply store recommended two single pole 20A GFI's sharing a neutral? Does this make sense. I have a 40amp double pole in the main feeding the sub via the sub panel...

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search