    Furnace will not fire
    I took the cover off and noticed the red light was blinking
    2 times is there any way I can fix this myself or do I need to call someone
    XenoSapien's Avatar
    XenoSapien Posts: 627, Reputation: 42
    Senior Member
     
    #2

    Nov 6, 2007, 05:28 PM
    There should be some sort of code sheet that tells you what the amount of blinks mean. Take a look at the inside of a paneling or the manual itself.

    XenoSapien
    coldniowa's Avatar
    coldniowa Posts: 6, Reputation: 1
    New Member
     
    #3

    Nov 6, 2007, 05:37 PM
    Yes it says the pressure switch is open, should it be closed
    eschuen's Avatar
    eschuen Posts: 62, Reputation: 6
    Junior Member
     
    #4

    Nov 6, 2007, 06:07 PM
    For starters check your exhaust and intake pipes for any obstruction.
    Next, your pressure switches have rubber tubing going to them. For starters disconnect the tubing and blow and suck into them. You should hear a clicking from the switch. They may be stuck and this is a starting point.
    coldniowa's Avatar
    coldniowa Posts: 6, Reputation: 1
    New Member
     
    #5

    Nov 6, 2007, 06:23 PM
    Ok I did that, It did click once. It is a fairly new furnace
    Aprox 3 years old. From Nordyne
    XenoSapien's Avatar
    XenoSapien Posts: 627, Reputation: 42
    Senior Member
     
    #6

    Nov 6, 2007, 07:13 PM
    Is the warranty active or void?

    XenoSapien
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #7

    Nov 6, 2007, 07:27 PM
    Is the inducer coming on? It is the small blower near the pressure switch. The purpose of the pressure switch is to keep the furnace from firing if the inducer isn't running. See https://www.askmehelpdesk.com/heatin...ons-58313.html Under sequence of operations it describe each step the furnace goes through on start up.

    If the inducer is running and you get the open pressure switch code, the switch maybe bad.
    coldniowa's Avatar
    coldniowa Posts: 6, Reputation: 1
    New Member
     
    #8

    Nov 7, 2007, 02:24 PM
    The warranty ran out last year.. and No the inducer
    Or blower does not come on Is there any way to tell
    If the pressure switch is bad..
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #9

    Nov 7, 2007, 03:02 PM
    OK, you need to see why the inducer isn't running. Could be a bad relay on the control board, hard to identify, and expensive to replace. Try jumpering power to the inducer motor. If it runs, likely the board is bad. If not, the motor or connections are bad.
    coldniowa's Avatar
    coldniowa Posts: 6, Reputation: 1
    New Member
     
    #10

    Nov 7, 2007, 05:07 PM
    Could you tell me how I would do that..
    Sorry, not very smart when it comes to furnaces
    But I appreciate all your help. I am finally starting to understand
    Some of this
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #11

    Nov 7, 2007, 05:58 PM
    To do simple checks like this you do need some tools. A test light, a meter, or a voltage detector might be the best place to start with. I came across the niftiest gadget for trouble shooting, a voltage detector. They work through the insulation of wires. There are several brands. I have a GB Instruments GVD-505A, less than $15 at Home Depot. Touch it to a hot wire, and the end glows red. Find the doodad that lights it on one side, and not the other, and you have the culprit. You do not have to open up housings and expose electrical contacts. You are looking at where your hand is, not where the meter is. Most people are capable of doing repairs and will get it going and not get hurt if they use a little sense. The voltage detector makes it even easier.

    Have you browsed through the sticky enough to understand where the inducer is? They are hidden inside the vent. Some of them have a black wheel on the outside that turns when it is running. You should be able to follow the wires from it back to the control board. With the voltage detector I suggest, with the thermostat set for heat, and the cover off, hold in the door switch while probing the wires that run to the inducer. If you don't have voltage, try wiggling the plug on the board a little. If you still don't have voltage, likely the board is bad. If you have voltage, likely the motor is bad.

    With a volt meter, you can check the contacts on the board, where the inducer plugs in, for 120 volts
    coldniowa's Avatar
    coldniowa Posts: 6, Reputation: 1
    New Member
     
    #12

    Nov 7, 2007, 06:23 PM
    I will do that. Thank you very much for
    All your help. I will let you know what I find out
    beekay's Avatar
    beekay Posts: 4, Reputation: 1
    New Member
     
    #13

    Nov 7, 2007, 08:01 PM
    I own a Payne (18 yrs old -- made by Carrier and Day/Night Co.) Heat/AC rooftop mount unit. I have done most of the maintenance on it over the years, including replacing defective parts. The AC works fine as does the blower. The heat unit started acting up recently. The unit would fire up and then sometimes it wouldn't. When the flame did not start, I tapped on the intake pipe and gas manifold and then it would fire up. Now, it won't fire up at all. I get the clicking for the pilot start, but am not getting any gas to the burners (they will not ignite). Gas is getting into the "valve" but not getting to the pilot or manifold. Any ideas?? Please help
    Thanks much.
    Brian
    toni11's Avatar
    toni11 Posts: 3, Reputation: 1
    New Member
     
    #14

    Nov 8, 2007, 11:41 AM
    How much is a typical control board... do I have to order or I can buy a board at Lowe's or Home depot?
    beekay's Avatar
    beekay Posts: 4, Reputation: 1
    New Member
     
    #15

    Nov 24, 2007, 06:07 PM
    coldniowa----
    First of all, you need a voltmeter. You can get one for your purposes for less than $10.00. If no voltmeter, you should have 2 wires connecting to your inducer motor. Purchase or make up a jumper wire with small alligator clips on both ends. Turn on unit and locate a hot wire. Connect jumper wire to a hot wire and then to terminal on inducer motor to supply power. Make sure you hook up another wire to a good ground (bare metal) on other terminal of inducer motor. If still no power, and you are sure you have done these steps, check the thermal limit switch. It's on the blower cage that turns, and should have a reset button. Hope this helps.
    beekay's Avatar
    beekay Posts: 4, Reputation: 1
    New Member
     
    #16

    Nov 24, 2007, 06:19 PM
    toni11 ----
    How much is a typical control board... do I have to order or I can buy a board at Lowe's or Home depot?

    toni11----
    Unfortunately, for the majority of parts, a non-hvac (Heat.-Vent.-AirCond.) person cannot purchase parts for themselves. The parts are not available at hardware stores --- only at local suppliers who sell to hvac workers and companies. The reason for this is the fact that too many people are not smart when it comes to these systems, and the supplier does not want to have a liability issue if a person blows or burns up their house.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Self ignitor furnace won't fire [ 1 Answers ]

Our Coleman Evcon furnace is reluctant to fire the first time in fall. The ignitor glows but then the gas will not fire. Is something dirty, is this something I can service myself? Appreciate any help, thanks.

Furnace catching fire [ 1 Answers ]

Our heating furnace is powered by propane gas. There is a weird smell coming from it and when I relit the pilot light & turned the thermostat to "on" fire started blowing out of the furnace. Please help... could we have carbon monoxide in our home? There is also soot caked on the inside of...

Carrier furnace does not always fire [ 1 Answers ]

Have a carrier weathermaker 90% HIGH EFFICINCY FURNACE ,this a spuratic problem.Sometimes when the stat calls for heat I can here the vent van come on and sometimes will run for 15-20 minutes, then the furnace fires up.some times it won't fire at all, shuting off the power switch on the side of the...

Goodman Furnace won't keep fire up [ 2 Answers ]

I have a Goodman GMP100-5, age uncertain, maybe 6 years. The burner fired up for 7 seconds or so and turned off. After 3 cycles it went off. The status light blinked once. Since the gas fired OK. I replaced the flame sensor. It still does the same thing after the flame sensor replacement. It is a...

Furnace will not fire [ 1 Answers ]

I have a comfortmaker GNJ075n12a1 80% furnace installed in 96 the igniter come on and the blower comes on and the system cycles a couple of times before the control locksout on during this time the gas valve is not energizing to fire the furnace if you shut the system down for a couple of...