    Spa disconnect
    Does the spa box count as the disconnect or does there need to be one somewhere else? I am building a 12'x12' gazebo and the spa box will be on the outside. The wiring is going to come up through the concrete in steel conduit. To add a disconnect somewhere else would put it somewhere in the yard.
    Thanks!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 16, 2007, 06:41 PM
    Needs to be within sight off each other, many inspectors will rely on the commercial code and want it at the unit. Many new spas come with a disconnect built in. Having a disconnect closer allows the GFI to be closer for convenience, and does not detect the capacitance of a long cable run,which would cause nuisance tripping.

    Just cannot be closer than 5 feet to the tub.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

A/C Disconnect switch [ 7 Answers ]

I am having a 36,000 BTU split system installed. This unit is 230/208v with 30 amp breaker. Instead of using the pull out style or lever style disconnects, would it be safe to use a 30 amp 120/277v a/c double pole toggle switch mounted in a appropriate weather proof box as my disconnect?

SPA disconnect switch grounding wire requirement [ 1 Answers ]

I'm installing a 240V/60A SPA approximately 85 feet from the house service panel. I'm going to run 3 individual #6 conductors (THN or better) from the service panel to the SPA GFI disconnect box via 1 inch PVC conduit. The SPA is about 7 feet from the disconnect box. The disconnect box instructions...

Locking disconnect [ 1 Answers ]

What is locking diconnect with respect to starters.

Another disconnect question. [ 5 Answers ]

Greetings all... I've spent the last few minutes reading several questions about main disconnect panels/breakers outside the home ( between the meter and breaker box ). I had been thinking about inquiring about having such a device installed here in my NC home. You see, my house is very old,...


View more questions Search