    Spa disconnect
    Does the spa box count as the disconnect or does there need to be one somewhere else? I am building a 12'x12' gazebo and the spa box will be on the outside. The wiring is going to come up through the concrete in steel conduit. To add a disconnect somewhere else would put it somewhere in the yard.
    Thanks!
  • Oct 16, 2007, 06:41 PM
    tkrussell
    Needs to be within sight off each other, many inspectors will rely on the commercial code and want it at the unit. Many new spas come with a disconnect built in. Having a disconnect closer allows the GFI to be closer for convenience, and does not detect the capacitance of a long cable run,which would cause nuisance tripping.