New Member
|
|
Sep 29, 2007, 11:07 AM
|
|
Running a 20-amp circuit
I am building a home theater and am now going to be requiring 2 20-amp circuits for certain amps I will be putting in.
My dad is an electrician with a master's license (a master electrician, if you will) that he has had for about 30 years. I think he'd be able to do it, but I still want to know about it. Thanks. ;)
|
|
 |
Senior Member
|
|
Sep 30, 2007, 03:45 PM
|
|
You want to know about what?
|
|
 |
Uber Member
|
|
Sep 30, 2007, 06:13 PM
|
|
You must have room in your breaker box for more circuits. You can always add tandem breakers, but most boxes specify a maximum number of poles, which may mean you have to add a sub panel. For a 20 amp circuit, you put in a 20 amp breaker and run # 12-2 with ground. Usually in a residence you use NM-B. It is a bit of a pain to retrofit into existing walls. You can tack up surface mount conduit instead. Finally, you install a box with the outlet. In a retrofit you can use old work boxes that clamp to the drywall and don't have to be nailed to the studs. You dad will know the details I left out.
|
|
 |
Printers & Electronics Expert
|
|
Oct 1, 2007, 11:17 AM
|
|
Also, if you are running 20A through 12/2 you must use 20A receptale in order to be code compliant. If your dad is actually a master sparky, then you should be able to have this conversation with him.
|
|
 |
Senior Member
|
|
Oct 1, 2007, 12:44 PM
|
|
Still the question remains. Yet, the two post are a start!
Lab are you an electrician?
|
|
 |
Uber Member
|
|
Oct 1, 2007, 12:52 PM
|
|
No I never claimed to be. I stick to what I know, which in some cases is more than some other people that sound like they are doing wiring jobs. Actually I mostly stay out of electrical questions unless I see a poor answer. It sounded like the guy wanted the basics, and I was able to give them.
|
|
 |
Uber Member
|
|
Oct 2, 2007, 06:26 AM
|
|
If in conduit, you may be able to pull 3 new wires from panel to new location(2 hots, a 1 neutral) both hots need to be on opposite phases to share neutral, or neutral could be overheated or burned up by seeing up to 40 Amps(total to the 2, not the difference of the 2.
If you ran 12-3, you could have 2 circuits as well. Still need to be on opposite phase.
If for some reason, you want 2-20 Amp circuits on 1 duplex receptacle, break the "Hot" tab on receptacle. You would need a 2 pole breaker so it breaks both 120 volt circuits.
|
|
 |
Printers & Electronics Expert
|
|
Oct 2, 2007, 07:06 AM
|
|
Whoa, Sratman - You have just told him to wire 220/240.
OK, Can you use Retrofit boxes? The answer is Yes, that is the recommended method. Certainly, if the wires are run to the outlet, are 12/2 then you can use the existing wires. However, if the wire is #14AWG, back to a 15 Amp breaker, then NO! If you want to draw 20 Amps, then you must replace the breaker in favor of a 20 Amp breaker. The wire must be upgraded to 12/2 or 12/3 and the outlet must be changed to a 20 Amp rated outlet. This is mandated by the NEC Code. Running #14 cable carrying 20 Amp is asking for a fire.
|
|
 |
Uber Member
|
|
Oct 2, 2007, 07:32 AM
|
|
Donf,
You may have missread, like you say use 12-3, that is 2 120 volt 20 amp circuits(multicircuit).
Don't know where the #14 wire was mentioned?
Where I live, we haven't been able to use #14 or aluminum for almost 30 years,
A supplement to the NEC. I will NEVER suggest #14 or Aluminum wire(Have seen to many problems with aluminum, from salt air and corrosion. Some areas are fine. I like Copper.
|
|
 |
Ultra Member
|
|
Oct 2, 2007, 08:01 AM
|
|
If he is running conduit, single strain wires wires would pull easier than 12-3 cable
Each circuit requires a hot, neutral, and ground run from the breaker to outlet
If you pull only 3 strained wires through 1/2 inch conduit it is fairly easy
Pulling 6 stranded wires is not that difficult if properly lubricated
The biggest problem is too many bends -- help is good when pulling wires
|
|
 |
Uber Member
|
|
Oct 2, 2007, 08:18 AM
|
|
Good thing you have your dad to count on.
|
|
 |
Printers & Electronics Expert
|
|
Oct 2, 2007, 08:36 AM
|
|
OK - Let's restart here!
Arande2 It would be real nice if you would chime in and level set this question. Stratman, Yes, I agree with you on the use of #14 wire, however, we cannot see the wire Arande2 physically has at his location, so I asked the question.
What I believe has been stated and asked for:
1) Building a Home Theater and needs to run two 120vac/20amp outlets.
My first questions - Is this new construction or are you making over a room?
Are the outlets in the room 15 Amp outlets or 20 Amp outlets?
What is the source for these outlets 15 Amp on panel box or 20
Amp on panel box?
2) Do you require a single 20 Amp run to a 20 Amp outlet or split double outlet? Or do
You require two independent runs to two 20 Amp outlets
If the panel box for this run is 20 Amp breaker, through 12/2 cable to 20 Receptacle you are fine. However, if the Panel source is 15 Amp over #14 cable to a 15 Amp outlet, you are in trouble. To be code complaint, you must install a 20 Amp breaker, run 12/2 or 12/3 wire and install a 20 amp outlet.
The mention of #14 AWG came from me because I wanted to make sure that 12/2 or 12/3 are in the wall
|
|
 |
Uber Member
|
|
Oct 2, 2007, 08:40 AM
|
|
The original poster asked a broad, general question, which was reponded to with a question for more detail by Washington.
No response from the original poster, but plenty of discussion about who knows what.
Poster has an electrican.
This question is closed.
|
|
Question Tools |
Search this Question |
|
|
Check out some similar questions!
Running two 100 amp main panels from a 200 amp service
[ 27 Answers ]
Greetings!
I live in a rural country area. The electric company will be installing a pole, meter, and 200amp service with disconnect at pole. (It will require 50 foot run of service cable from pole to main load center in mobile).
Currently the double wide has a General Electric 100amp Main...
20 AMP Circuit with 15 AMP Receptical, is this OK, and in code?
[ 5 Answers ]
This is sort of similar to the other thread, but my problem is the house I bought is wired with 12, all the breakers are 20AMP except for the 30AMP for the AC and Dryer. When me and my dad were changing the power recepticals, which were 15 amp, someone told us that we should have 20 recepticals, or...
Converting 15 anp circuit into 20 amp circuit
[ 1 Answers ]
I just bought a treadmill. The problem is it doesn't work where I want it to. It can only run on 20 amps but all my outlets use 15 amps. It keeps tripping the breaker. Can I easily convert my outlet to a 20 amp?
Bath tub shower spout & head running water running at same time
[ 1 Answers ]
I started with a slight dripping problem(sayko system).i decided to replace all 3 stem assemblies together as they all were about 18 years old.after reassembling the new stems(danko brand),turned on the water supply & checked faucets.hot & cold worked fine but when the shower was turned on,water...
View more questions
Search
|