    Wire and coduit size
    What size wire and conduit is needed for a 125 amp, 120/240 volt, 4 wire , sub panel?
    Flying Blue Eagle's Avatar
    Flying Blue Eagle Posts: 2,056, Reputation: 225
    Ultra Member
     
    #2

    Sep 29, 2007, 08:52 AM
    I'd use no less then #6, Don't forget your copper ground from main panel to new sub panel:::::
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Sep 29, 2007, 09:50 AM
    I just wired up one that way, but I am feeding it from only a 60 amp breaker. I think the full 125 amps needs something heavier.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Sep 29, 2007, 10:11 AM
    Min size is #2 copper,or #1/0 aluminum for residential feeder.

    Should not guess at wire sizes.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Sep 29, 2007, 10:50 AM
    As I said, I thought you needed heavier wire. tkrussell knows you do. He knows the conduit size too, but may have let the #6 wire answer distract him from saying so.
    Flying Blue Eagle's Avatar
    Flying Blue Eagle Posts: 2,056, Reputation: 225
    Ultra Member
     
    #6

    Sep 29, 2007, 03:10 PM
    Hey tkrussell:::- I hit the wrong key , I' just learning on the type writer keys . In fact I' m still doing what my son said, 9hunt sand peck. but I'mtrying.After I get done I look over whaty I just done and try yo correct my mistakes. I'm not going to redo thisd one F.B.E.
    danar's Avatar
    danar Posts: 69, Reputation: 2
    Junior Member
     
    #7

    Oct 7, 2007, 03:53 AM
    You Can Also Consult Your Nec For Your Wire Ampacities And Sizes Of Your Conduit...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size wire? [ 3 Answers ]

For a run of #2 electric wire, in conduit, what size neutral and what size ground wires should I use? It's about a 50 foot run.

Wire size etc. [ 1 Answers ]

Back to Honduras, where the NEC don't apply.. I am installing a 150 amp service.. and it is about 100 ft from breaker panel to meter, and about 50 ft from meter to utility pole connection.. These people commonly use aluminum, and # 2 awg is the largest I can find.. Does anyone think this is...

Wire size [ 2 Answers ]

I am wiring a barn/shop fed by a 100 amp service. Some of the outlets may be over 70 feet from the panel (all will be 20 amp breakers). Should the wire size I pull in for these outlets be 10awg rather than the normal 12awg? My question relates to voltage drop. The shop is about 50'x 70'. Two big...

Wire size [ 3 Answers ]

What size wire should you use for a 125 amp three phase circuit? How do you figure that for future reference?

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search