    The minimum wire size for my hot tub with a 40 amp GFCI is #8 gauge/4 wire, but I will have to have about 125' of wire to go from my breaker box to the hot tub. Is the rule of thumb for a wire 100' or more, to increase the size of wire to # 6 and a 50 amp GFCI ? And can I assume that I cannot wire the hot tub and plug into a 30 amp # 10 wire outlet that already exists since it is only rated for 30 amp?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 22, 2007, 03:10 AM
    If the tub draws more than 26 amps or 6240 watts, a 40 amp circuit is needed.

    Assuming the max steady load of 32 amps or 7680 watts for a 40 amp circuit, the #8 will produce 2.5% voltage drop, the max recommended is 3%.

    If your supply voltage does sag any, this percent will increase. Plus the motor will have starting current to consider.

    Upsizing to #6 for this length would be good. Still only need a 40 amp circuit breaker thou.

    You can start the circuit at the panel with a standard breaker, and have the GFI at the tub, will prevent nuisance tripping due to circuit length and convenience of having the reset close to the tub.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hot tub wiring [ 1 Answers ]

:confused: I have a hercules pro pak 733034 electric supply box for my hot tub. It has 4 wires. 2 blue and 2 black. The wires come into the contol box and the 2 blue go to a screwed connection and the one black goes to white wires in which one white wire goes to the gfi outlet on the front cover....

Wiring hot tub [ 7 Answers ]

When running wire from electrical box to hot tub should I use conduit (outdoor) or is there under ground rated 240v wire. Also what is appropriate wire size?

Wiring of a hot tub. [ 1 Answers ]

We just had a free hot tub giving to us. We already have 220 in our house. We just need some help getting it wired. It is an older Jacuzzi model. Can some one provide us with a diagram or instructions.

Hot tub wiring [ 1 Answers ]

I'm wiring a subpanel for my hot tub. I know the white wire from the breaker goes to the neutral bar, but does the neutral wire from the hot tub connect to the neutral bar or the neutral terminal on the GFI breaker?

Hot Tub wiring [ 2 Answers ]

I installed a gfi breaker at the main box but wanted to double check my work. The neutral white wire from breaker goes to the ground bar. But does the solid copper ground lead go their also? Thanks


View more questions Search