Senior Member
|
|
Sep 6, 2007, 04:17 PM
|
|
Calculate A/C
Anyone wants to take a shot.
I seen this posted somewhere else, and was amazed by the answers I seen. Yet would love to see what you get.
The unit is a Residential room Window Air Conditioner--with cord and plug. (Cord and Plug has a trip button)
Nameplate:
Volatge 230/208
Watts 1850/1800
Amps 8.3/9.0
Heating:
Watts 3,670/3100
AMPS 16/15
Question:
-What size conductor can I run from the panel to a 240V receptacle
-What size breaker do I need
|
|
 |
Uber Member
|
|
Sep 6, 2007, 04:44 PM
|
|
OOH,OOH OOH,I know I Know...
I will be interested in seeing the answers also. I would like to also know how this is calculated, why, what code section this falls under.
For clarity I assume this is a combination unit with heat and AC built all into one appliance.
I love riddles.
Bet you thought I was going to answer. Ha, fooled you.
Remember everyone, there is a link in the Read First sticky note at the beginning of the electrical forum to the NEC with instructions of how to get there.
Washington, I would be interested in seeing the other answers you found or received. Even some of the best electricians I have met have problems understanding HVAC.
|
|
 |
Senior Member
|
|
Sep 6, 2007, 06:07 PM
|
|
By the way, the run is 40 feet from the panel!
TK,
I will post one of the answers!
Thanks!
|
|
 |
Uber Member
|
|
Sep 6, 2007, 06:38 PM
|
|
At the risk of getting ridiculed 12 Ga, 20A; So the cord has a GFCI - So?
Assumption: Both can't run at the same tme
|
|
 |
Uber Member
|
|
Sep 7, 2007, 12:34 PM
|
|
Well I see you received only one answer, which happens to be correct.
I did not get any reason or code section.
The assumption is correct, that is why I was hoping for the code section.
AC units have been coming with Arc Fault protection built into the power supply cords.
Washington, do you agree with the #12 wire and 20 amp CB?
|
|
 |
Uber Member
|
|
Sep 7, 2007, 01:05 PM
|
|
Ok, I didn't want to give it away. A/C may have mislead someone. It was a combo unit and I assumed that both would not be on at the same time, so the highest load prevailed. I didn't bother normalizing the load to 240 V. We know by experience that 12 GA is good for 20 A (An ampacity table verifies), but but just to use the 40' or really 80', looked at the voltage drop in the leads. It didn't appear excessive. Chose the next standard breaker of 20A.
|
|
 |
Senior Member
|
|
Sep 14, 2007, 04:59 PM
|
|
 Originally Posted by tkrussell
Well I see you received only one answer, which happens to be correct.
I did not get any reason or code section.
The assumption is correct, that is why I was hoping for the code section.
AC units have been coming with Arc Fault protection built into the power supply cords.
Washington, do you agree with the #12 wire and 20 amp CB?
Sorry, been busy trying to find work for my company. Things have slowed down greatly!
Yeah, I agree. Heck the answer was in the pudding. Personally, I still would have ran #10, but that's me.
I look @ 440.32/440.62 (A)/ and 210.23(A) and (B) depending. Or just look at the cords rating :)
|
|
 |
Uber Member
|
|
Sep 15, 2007, 05:39 AM
|
|
Correct regarding 440.62, as the unit is a room air conditioner, and does fall under Article 440 VII, Section 440.60.
Section 440.32 does not apply.
#12 is the minimum size allowed, exceeding the code is always a good practice.
Depending on the length I may install #10, but for most normal runs, say 50 feet and under, I would sleep fine with #12, and pass the cost savings of copper, such as it is today, onto the customer.
The trip button is the Arc Fault required to be factory installed as per Section 440.65.
If this was a permanently installed heating/air conditioning unit, none of these sections would apply.
|
|
 |
Senior Member
|
|
Sep 16, 2007, 10:15 AM
|
|
 Originally Posted by tkrussell
Correct regarding 440.62, as the unit is a room air conditioner, and does fall under Article 440 VII, Section 440.60.
Section 440.32 does not apply.
#12 is the minimum size allowed, exceeding the code is always a good practice.
Depending on the length I may install #10, but for most normal runs, say 50 feet and under, I would sleep fine with #12, and pass the cost savings of copper, such as it is today, onto the customer.
The trip button is the Arc Fault required to be factory installed as per Section 440.65.
If this was a permanently installed heating/air conditioning unit, none of these sections would apply.
Exactly! Note that I said I look at! :)
There's always some considerations, if the window A/C doesn't meet the requirements.
I agree TK!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
How do I calculate the following
[ 2 Answers ]
Owens Orchards sells apples in a large bag by weight. A sample of seven bags contained
The following numbers of apples: 23, 19, 26, 17, 21, 24, 22.
a. Compute the mean number and median number of apples in a bag and verify.
Calculate A/c requirements
[ 1 Answers ]
What formula do I use to calculate Gas/Pack (cooing-heating) size requirements for a 1700 square foot masonry home in the southwest?
How many years to calculate
[ 1 Answers ]
Trigger company purchased a machine that has a manufacturer's suggested life of 15 years. The company plans to use the machine on a special project that will last 11 years. At the completion of the project, the machine will be sold. Over how many years should the machine be depreciated?
View more questions
Search
|