Originally Posted by tkrussell
Correct regarding 440.62, as the unit is a room air conditioner, and does fall under Article 440 VII, Section 440.60.
Section 440.32 does not apply.
#12 is the minimum size allowed, exceeding the code is always a good practice.
Depending on the length I may install #10, but for most normal runs, say 50 feet and under, I would sleep fine with #12, and pass the cost savings of copper, such as it is today, onto the customer.
The trip button is the Arc Fault required to be factory installed as per Section 440.65.
If this was a permanently installed heating/air conditioning unit, none of these sections would apply.