    Current capacity of transformer
    If I have got a 3 phase 750 KVA tranformer of 6.6KV / 380 V , what is the max output current capacity per phase. How is it calculated.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 26, 2007, 05:48 AM
    Line Current = 750000 VA / (380 V x 1.732) = 1140 amps per phase
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Aug 26, 2007, 12:19 PM
    1.73 is the square root of 3 BTW.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Dryer capacity [ 2 Answers ]

What is the capacity of Kenmore Dryer Model No. 110.60052990, Serial No. MK2007703

Current & Non-Current Assets [ 3 Answers ]

Why is classification of Assets into Current & Non-Current necessary? Or not necessary?

Capacity of old panelboard [ 3 Answers ]

Hello, I am checking to see if the panelboard in the old building can handle my load (considering a restaurant in this building) The old square-D panelboard label reads: Power <<<< >>>> lights ------------------------------------ 90 << bus amp>> 175

Mean capacity [ 1 Answers ]

A particular type of plastic soap bottle is designed to have a capacity of 15 ounces. There is a variation in the bottle manufacturing process. Based on historical data, suppose that the bottle capacity can be reasonably modeled by a normal distribution with a mean of 15 ounces and a standard...

Amperage lost from a current transformer to utility's electric meter(?) [ 2 Answers ]

I work for an Electric utility. Have noticed that the actual amperage running through a phase does not match the amperage being sent to the meter with it's proper multiplier from the current transformer (CT)? Example: phase A is using 83 amps. The X1 tap to the meter from the current...


View more questions Search