    GFI Breaker pops
    I have a 20a gfi breaker that keeps popping.as soon as i flip it on ,it pops.we have had a lot of rain.need help please
    nauticalstar420's Avatar
    nauticalstar420 Posts: 3,699, Reputation: 423
    Ultra Member
     
    #2

    Jul 1, 2007, 10:25 PM
    My husband is an electrician so he can answer your question. What section of the house does the breaker control?
    brentc's Avatar
    brentc Posts: 4, Reputation: 1
    New Member
     
    #3

    Jul 1, 2007, 11:03 PM
    It contols about 6 plugs throughout 3 rooms.I Have changed the breaker and still triped.
    nauticalstar420's Avatar
    nauticalstar420 Posts: 3,699, Reputation: 423
    Ultra Member
     
    #4

    Jul 1, 2007, 11:08 PM
    There's probably a wire that's exposed and its grounding itself out or there's a wire arcing and its causing the breaker to trip.
    brentc's Avatar
    brentc Posts: 4, Reputation: 1
    New Member
     
    #5

    Jul 1, 2007, 11:20 PM
    So where should I start.Everything is unpluged and still pops right away,We had about 20 inches of rain.So Don't know for sure if that has a part in it.
    nauticalstar420's Avatar
    nauticalstar420 Posts: 3,699, Reputation: 423
    Ultra Member
     
    #6

    Jul 1, 2007, 11:25 PM
    I can't give you a step by step instruction on what to do because I cannot see the problem. Call a certified electrician to take a look at your problem right away, because if it is arcing it could be a fire hazard.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #7

    Jul 1, 2007, 11:37 PM
    It could be as simple as a bad GFI or a bad connection, if your not real familiar with electricity the best advice is to call in an electrician. It is hard to troubleshoot a problem without seeing, however there are a couple of good electricians on this site, and I'm sure they will review this thread.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #8

    Jul 1, 2007, 11:42 PM
    The GFCI operates by sensing the difference between the currents in the Hot and Neutral conductors. Sounds like you have a Ground fault downstream.

    You keep saying "rain"? Explain. Are your devices exposed to water?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #9

    Jul 2, 2007, 07:39 AM
    Disconnect wire from breaker, if it resets, problem likely downstream from breaker. Reconnect.
    If qualified, I would remove receptacle closest to breaker, Disconnecting wires. If breaker doesn't trip, power good to there(No Fault). Repeat till you find wires faulted.
    Can fault with hot to ground(or neutral), or neutral to hot.
    brentc's Avatar
    brentc Posts: 4, Reputation: 1
    New Member
     
    #10

    Jul 2, 2007, 07:44 PM
    There was moisture in the box.I Took breakers out and blow dried evrything,Switched gfi breakers and still poped.I Then put a 20 amp standard breaker and it will hold.I Talked to my electrician and he says as no plugs around countertops or b/r ,That is what he would do.We have had about 20 onched or rain,I Think moisture somewhere was making the gfi fault.So this where Iam at now,Everything looks good now.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #11

    Jul 3, 2007, 04:55 AM
    It may not be tripping breaker, but something may be getting warm, and drawing current.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

GFI Breaker Trips [ 1 Answers ]

Greetings all! I have a 15 amp GFI breaker that trips anytime something is plugged into any of the outlets on that circuit. I have used a circuit tester and it appears everything is normal but still when I plug anything at all into any of the outlets the breaker trips. What would cause...

Gfi breaker to outlet [ 3 Answers ]

Hi, I would like to know how to connect a GFI 4 wires circuit breaker to a outlet to be used for a air conditioner (220v). The GFI was used for a 220v spa now that the hot tub is not being used. I want to use the same breaker for a air conditioner. I purchased a outlet but it only has 3...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!