    Adding GFCI Breaker to Existing Subpanel
    I want to add a GFCI breaker to an existing sub panel (used to power a hot tub) so I can have a protected outlet on my patio. However, I'm confused as to how to wire in to the existing wiring.

    The existing sub panel has a double pole 50A breaker with 2 hot wires (red and black) and a neutral white wire plus a green ground. At the sub panel, the white wire and ground are ganged onto the same bus. I traced the wires going to the sub panel and verified the white is connected to the main house neutral, while the black and red come from another 50A 2-pole breaker on the main panel.

    My confusion lies with the white neutral being connected to ground at the sub panel. I thought that GFCI breakers require the neutral and ground to be separate. If so, how can I add a GFCI to this sub panel?

    Thanks,

    HDD
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 24, 2007, 08:58 AM
    At any subpanel, the neutral is to be insulated and isolated from the equipment ground, which is connected directly to the metal can of the panel box.

    The issue is anything beyond the main disconnect requires the neutral and equipment ground to be separated, not just GFI breakers.

    This really needs to be addressed and corrected.

    The neutral from the load or outlet connects to the neutral lug on the GFI breaker, The white pigtail neutral from the GFI breaker connects to the neutral bar in the panel.
    Harddrive's Avatar
    Harddrive Posts: 3, Reputation: 1
    New Member
     
    #3

    May 24, 2007, 09:08 AM
    Quote Originally Posted by tkrussell
    At any subpanel, the neutral is to be insulated and isolated from the equipment ground, which is connected directly to the metal can of the panel box.

    The issue is anything beyond the main disconnect requires the neutral and equipment ground to be separated, not just GFI breakers.

    This really needs to be addressed and corrected.

    The neutral from the load or outlet connects to the neutral lug on the GFI breaker, The white pigtail neutral from the GFI breaker connects to the neutral bar in the panel.

    So I take it the wiring in this sub panel is not done to code? I just want to make sure before I contact the company that did the work.

    Thanks,

    HDD
    Harddrive's Avatar
    Harddrive Posts: 3, Reputation: 1
    New Member
     
    #4

    May 24, 2007, 11:53 AM
    Quote Originally Posted by bhayne
    In Canada, there is a provision in the code that treats a separate building as a separate service even though it is fed from an existing service. In that case, the subpanel will have its neutral and ground tied together.
    Well, this is in the US (Colorado). Also, the sub panel is on the same building as the main, just on the opposite side. I believe the code requires the panel and breaker be within a close distance (5-10 feet) of the hot tub it services.

    Maybe I should start a separate thread to ask if sub panels can have their neutral tied to their ground?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    May 24, 2007, 12:36 PM
    While the subpanel and/or breaker does not need to be near the tub, a disconnecting switch must be "readily accessible and with in site" of the tub.

    Many times the GFI breaker is in a small subpanel, and is installed no closer than 5 feet of the tub , and acts as the disconnect also. Keeps the installation simpler, and saves buying an additional piece of equipment.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

GFCI Breaker vs Receptacle [ 1 Answers ]

I'm adding some 20A circuits in my garage/shop and know that they have to be GFCI protected. My question is this: Is there an advantage to using a GFCI breaker over just putting a GFCI receptacle in the first slot of the series? Thanks.

Adding subpanel [ 6 Answers ]

I have a 200A main panel in my garage and want to install a subpanel in my basement to feed 4 circuits (15 & 20 A). The best route I can find for the feeder wire is through the garage in conduit, then entering the basement through the concrete foundation. I have a couple of questions. 1. If I...

Adding subpanel [ 1 Answers ]

I'm converting my garage to a woodshop, so I need 220 service for the table saw and band saw, and potentially later the dust collector and compressor. Also I want to run a new circuit for lights, plus two 110 outlet circuits. That's a possible four 220 and three new 110 circuits. I've got a...

Gfci breaker popping [ 8 Answers ]

After installing a second outdoor fan, I tied into an existing fan under an enclosed porch.I decided it would be smart to install a gfci breaker to protect them (vs the standard breaker). The circuit is tied into my kitchen an outdoor spot lights. With all the individual light circuits either...

Gfci breaker [ 2 Answers ]

My question is I have a 50 amp GFCI breaker that I will be installing in the breaker box. I have another 50 amp GFCI breaker box that must be installed within 5 feet away from the hot tub. Is it OK to install both 50 amp GFCI breakers for this hot tub I realize I don't need two GFCI's but I...


View more questions Search