    Isn't UF for outdoors and THHN indoors? Also when you go to HomeDepot or Lowe's There big Hanging chart says "Outdoors use UF and with a 50 amp breaker use #8" ?

    Ok,
    Last question I hope. For my spa, Can I use THHN grade wire #6 copper(romex?)for outdoors if it is running through conduit ? And it is OK for a 50 amp breaker? Thanks
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    May 19, 2007, 01:53 PM
    UF is Underground Feeder, like romex. I would use #6 for 50 amp breaker
    #8 for 40 amp
    #10 for 30 amp
    #12 for 20 amp
    #14 for 15 amps.
    THHN is usually single conductors
    I would Use 2 # 6's for the hots, 1 #8 for neutral, and #10 for ground, and in PVC
    Use breaker at main Panel recommended for Spa. Also Needs GFI Protecton near Spa.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gfci spa panel tripping [ 4 Answers ]

I just installed a spa with 4 wires. The house is old and while the neutral & ground bus bars are separate in the spa panel, they are all on the same bar in the main panel. Do I need to install a ground rod by the spa panel to keep the gfci from tripping? (instead of running the ground back to the...

Spa wiring questions [ 4 Answers ]

I recently purchased a hot tub (spa). It calls for 6-3 with ground 240 volt 50 amp gfci breaker installed. I have almost completed the job and have some questions. I installed a 50 amp breaker in a subpanel in my laundry room and ran the 6-3 wire with ground down in the crawl space out to the...

Extending spa feed [ 2 Answers ]

I have existing 220v wiring (outdoors) for a spa that I want to extend another 15 ft. in order to hide the panel from view. Do I have to re-wire the run, or can I just extend it with a junction box and another 15 ft. of cable/wire? I'm in California, if that makes a difference. Thanks in advance...

Outdoor Spa and lighting [ 1 Answers ]

Dear all, Happy holiday's I have two 40amps in the main box that feeding the AC Unit. I would like to know if its possible and code pass in new Jersey, Piscataway. To tap into that conduit at a junction point and extend the required wires in a conduit 30-40 feet to a Spa 50/AMPS @ 240...


View more questions Search