    A/C Breaker
    As it got warm, I turned on my A/C to "cool" down a little. The fan came on, but it did not cool the house down. For whatever reason, I went to the garage to check the fuse box and saw the breaker was tripped. I turned it all the way off and then back on and it tripped as soon as I turned it own. This is the first time I have had this problem and I am the only one that has ever lived in this house. Why is it tripping and what can I do? I am burning up!!
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #2

    Apr 29, 2007, 09:04 PM
    Most commonly that would tell me either your compressor has a problem or may even be shot... there could be a short some where in the outside unit. How old is the system?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Apr 30, 2007, 06:04 AM
    Unless a wire has rubbed through its insulation or something, there is little you can do yourself. If you have an ohmmeter, you can disconnect the incoming lines and check each for being grounded or shorted to each other. If not, go to the load side. Each pole will have several wires. Remove all the wires from one pole and check to see if any of them are grounded. Also check for a short to the other pole. Note, the motor leads will have a fairly low, but not zero ohms reading to the other pole. If you find a bad reading, trace the wire to see where it goes. If you can't see a problem with the wire, chances are whatever it goes to is shot. If it is the compressor, you must call a pro. If the system is very old, it may be time to replace it.

    If you can't find a problem, there is some chance the breaker is bad.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!

Why does not a breaker close [ 8 Answers ]

Hi, I want a list of all reasons a breaker cannot be closed after a trip. Please give me all possible reasons. Regards, Ravi

#00 to 100a breaker [ 1 Answers ]

A friend of mine ran #00/3 from his house to his garage, but only wants a 100a service. What can I use to hook up #00 to a 100a main breaker, because I don't think the physical size of the wire will fit under the lugs in the breaker. Also I plan to run a #6 to a ground plate buried 3' outside the...

Breaker [ 5 Answers ]

I have low voltage landscape lighting plugged into an outside outlet. The total watts is about 500 and I am using a 600 watt transformer. The outlet is a GFI outlet and has a dedicated 20 amp breaker. Nothing else is on this breaker. Sometimes the breaker will trip. I have replaced the...


View more questions Search