    a/c residential
    Last summer when we had the really hot days of 90-100 degree temp outside my a/c system would not cool the house below 80 degrees inside and the unit would run constantly I decided today to check the system I put my guages on the cond. Unit and had a suction pressure of 45 and a discharg pressure of 185 the temp outside was 80 degrees and the inside house temp was 78 degrees , I checked the air temp above the evap coil and it was 52 degrees , why does this unit work OK until high outside temps.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Apr 23, 2007, 01:52 AM
    Clean the outside unit. It is probably dirty and when it is real hot cannot disapate the heat generated.
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #3

    Apr 23, 2007, 01:27 PM
    Is your filter and evaporator coil clean? With a 45 lb. suction line pressure, 185 highside pressure, 26 degree deference between the return air and discharge air temperature indicates low air flow through the evaporator coil. Your pressures are to low for a 80 degree day. Your system may also be overcharged, you need to do a superheat check after you check air flow. On a hot day when the system doesn't shut off and you have a 26 degree delta T. you are probably freezing up the coil.
    whbii's Avatar
    whbii Posts: 5, Reputation: 1
    New Member
     
    #4

    Apr 23, 2007, 09:58 PM
    Quote Originally Posted by JackT
    Is your filter and evaporator coil clean? With a 45 lb. suction line pressure, 185 highside pressure, 26 degree deference between the return air and discharge air temperature indicates low air flow through the evaporator coil. Your pressures are to low for a 80 degree day. Your system may also be overcharged, you need to do a superheat check after you check air flow. On a hot day when the system doesn't shut off and you have a 26 degree delta T. you are probably freezing up the coil.




    Thanks for your info jackt I will do a superheat check to see if the system is overcharged, my filter is clean I maintain that on a regular basis. And the condensing unit is clean as I usually wash that out at the beginning of every season.
    whbii's Avatar
    whbii Posts: 5, Reputation: 1
    New Member
     
    #5

    Apr 23, 2007, 10:01 PM
    Quote Originally Posted by hvac1000
    Clean the outside unit. it is probably dirty and when it is real hot cannot disapate the heat generated.




    Thanks for your info hvac1000 but the condensing unit was clean , I wash the coils out at the beginning of the season.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Residential boiler system [ 2 Answers ]

I have a residential boiler system in the house I bought. When I turned on the water supply to the boiler from the water system in the house, the T&P relief valve blew. I am assuming that this is because the water pressure in my household system (approx 70 psi) is too high for the boiler. The T&P...

Safer residential service. [ 3 Answers ]

Which is safer L1-110 L2-110 With center tap to ground Or L1-220 L2 gounded Thanks

Residential Land Contract [ 1 Answers ]

Is it possible to find an instructional package for residential real estate land contracts that may also contain forms for both buyer and seller? Hopefully at minimal cost.

Residential cleaning service [ 3 Answers ]

My name is Mari. I recently started a cleaning company. I have already cleaned serveral homes but I am having a hard time as to what I am suppose to charge. I do not have much experience in this field but thought it would be a good flexible job while I am in school. I have tried to get advice...

Residential Wire splicing [ 5 Answers ]

I am planning to relocate an old receptacle to a new wall location in our house. If I will splice a new wire to the old one and put it in a box, should that box be visible on the wall(with cover plate) or can I just hide the box inside the wall. Thanks.


View more questions Search