Originally Posted by JackT
Is your filter and evaporator coil clean? With a 45 lb. suction line pressure, 185 highside pressure, 26 degree deference between the return air and discharge air temperature indicates low air flow through the evaporator coil. Your pressures are to low for a 80 degree day. Your system may also be overcharged, you need to do a superheat check after you check air flow. On a hot day when the system doesn't shut off and you have a 26 degree delta T. you are probably freezing up the coil.