    240V circuit doesn't work
    My neighbors had asked me to take a look at the air compressor saying it didn't work. It turned out that their 240V outlet might be at fault. In the outlet, I measured about 120V between one hot wire and the ground and around 55V between the ground and the other hot wire. How can this be and what is wrong here? Thanks for any conment or suggestion. Best wishes, h.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Dec 19, 2014, 04:10 PM
    Bad connection/broken wire in the outlet box or possibly a bad breaker. Should measure 120-120 /240 between both hots.
    InfoJunkie4Life's Avatar
    InfoJunkie4Life Posts: 1,409, Reputation: 81
    Ultra Member
     
    #3

    Dec 20, 2014, 10:24 AM
    The outlet itself may need replacing. Its not uncommon that older outlets fault after years of use creating a bad connection. I would not recommend plugging anything else into it as it can cause damage to some equipment.
    EncoreWirePaul's Avatar
    EncoreWirePaul Posts: 1, Reputation: 2
    New Member
     
    #4

    Dec 30, 2014, 01:18 PM
    @harum -

    Firstly, verify the volt meter you are using is working properly on a known 240V (nominal) circuit. If this is the case then chances are you have either a bad plug or one leg of your branch circuit has come loose back at the panel.

    Secondly, find the circuit breaker that supplies power to this receptacle in question and verify at the source that you have 240V (nominal) between legs at the circuit breaker... if you get the same reading back at the circuit breaker then you can begin to worry... as a leg in your panel might have been dropped or come loose somewhere. If you get 240V at the panel and not at the receptacle then you have found the problem.

    Hope this is helpful.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What circuit breaker should I use for a 240V 1.6 amps [ 4 Answers ]

What circuit breaker should I use for a 240V 1.6 amps

AC doesn't work even 240v on condenser and inside unit [ 2 Answers ]

AC doesn't work, I check the power to condenser and blower unit and those are OK. Will it cause by transfomer? In the beginning my ac was working fine except not cool enough so I check the evaporator inside and I found it only half cool and half not cool. So I doubt that I might connect the wire...

Converting 240v circuit to a 110v circuit [ 6 Answers ]

I have a 240 circuit, to make it a 110 circuit. I need to remove one of the hot wires?

Extending a 240v dryer circuit [ 5 Answers ]

I have a simple question that I most likely already know the answer to, but I'd like to verify it anyway. I am moving an electric dryer from the basement to a newly finished laundry room on the first floor. I need to extend the 10-3 line from the current location to the new location, which is a...

240v Electrical circuit testing [ 1 Answers ]

I have replaced a celling light in my kitchen. The replacement light has a stainless steel casing, however the wiring circuit in the house has no earth at the celing, so I have not connected an earth. It has 2x black wires , 2x red wires ( switching & connected together ) & 1x black wire with a red...


View more questions Search