    AC doesn't work even 240v on condenser and inside unit
    AC doesn't work, I check the power to condenser and blower unit and those are OK. Will it cause by transfomer?
    In the beginning my ac was working fine except not cool enough so I check the evaporator inside and I found it only half cool and half not cool. So I doubt that I might connect the wire to my thermostat wrong, cause there's a blue wire(connect to common from board) I connected to my thermostat's. After that the condenser unit stop working first. And now the inside unit doesn't work as well. Can someone help? Thank you!
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Aug 24, 2009, 03:14 PM
    Look see if you have a fuse automotive type normally 3 amp,in the circuit board of the furnace,, if not one or it checks OK,, check the ourput side of the transformer ?with door button pushed in ,for 24 volts,

    You made a comment about connecting a blue wire, have you been messing with the tstat or wireing to the tstat? If so you may have fried the transformer

    Let us know what you find
    bonnie53's Avatar
    bonnie53 Posts: 4, Reputation: 1
    New Member
     
    #3

    Aug 24, 2009, 08:58 PM

    I have a lennox air conditioner HS26 series 3 ton. I have had trouble with the unit out side running. I had to replace the condenser, fuses and breaker. Worked great for two months. Now the unit won't run outside again. I had this problem off and on. When the unit cools down the unit outside will start up again. What could be wrong. .

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can uReplace a 10 seer ac condenser w/a 13 seer w/o changing the inside 10 seer unit [ 8 Answers ]

We have a 10 seer 2.5 ton heat pump outside condensing ac unit, that sprung a leak that cannot be repaired. We have had 5 repairmen come out and look. 3 of them say we have to replace the inside 10 seer 2.5 ton compressor and furnace as well. 1 of the 5 says we can just replace the outside unit...

AC Inside Blower Stops, Condenser runs continuously Until Entire Unit shut off & Reset [ 6 Answers ]

I have a Trane compressor outside. The unit comes on and the interior blower comes on for a few hours and then stops blowing. I tried to turn on the fan via the thrmostat and it does not work when it shuts down but otherwise works fine so its not a wiring problem. The outside unit continues to...

Replacing AC condenser's 40A 240v power wire from main to the unit [ 4 Answers ]

I am in the process of replacing our AC condenser's wires which powers the outside unit From main breaker. The existing 25+ years old wore out and damaged wire is romex 8/3 with ground on a 40A 240v dual-breaker. The AC guys when installed the unit, Connected the BLACK and RED to the 40A...

Can I connect new outside unit to older inside unit for a heat pump? [ 2 Answers ]

I have a heatpump system. The outside unit is very old and is different manufacturer than the newer (9yr old) inside unit. Outside unit has gone bad. Can I connect a new TRANE Outside unit with SEER of 13 to my 9 year old TRANE inside unit with SEER of 10 which still seems to be working...

Outside unit doesn't come on when thermostat turns inside unit on so no heat? [ 1 Answers ]

My thermostat will trip my heater to turn on. The inside blower turns on but the outside unit doesn't turn on. I can get it to go by turnign off the unit at the thermostat and waiting a minute. I turn it on and off until I hear the outside unit turn on. The problem is when the Thermostat turns if...


View more questions Search