    Tray Cable Questions
    Good morning!I'm trying to figure out the difference between tray cable types and tray cable ratings. The information I have has the types as, TC, VNTC, PLTC, ITC, XHHW, WTTC. The ratings I have are TC, -ER, WTTC.The questions I have are:1. What is the difference between tray cable types and tray cable ratings? As I understand it, ratings tell you what the cable is approved for and for what applications. Types are the actual specifications of the cables. Is this correct?2. What are the NEC requirements for tray cable to meet type XHHW?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 22, 2014, 06:04 AM
    Rating (Listed) = amperage , Type = insulation

    "X" = insulation material makeup. "HH" = high heat, 90C
    "W" = wet areas. Normally this type of cable can be used in either a wet or dry location.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Nov 22, 2014, 07:05 AM
    Ok, I looked up type XHHW cable in NEC 310.104(A) for you.

    It is a flame retardant, moisture resistant, thermoset insulated cable. It has temperature listings of 90C in dry or damp locations. In wet locations, the temperature cap is 75C.

    Wire type XHHW-2 can be used at 90C in dry, damp or wet locations.

    The temperature listings translate to the amperage column to use in Table 310.15(B)(16).

    For example 90C, 12 AWG cable, type XHHW is listed at 30 amps max in the 90C column. While in the 75C column its max amperage is 25 amps.


    Type XHHW-2 is 30 amps. Regardless of the location.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What type of cable do I need ser/ sur for 200amp service cable [ 2 Answers ]

I know I need 4/o alu for 200 amp but do I use ser or sur?

I replaced the cable, cleaned & lubed the deck parts, works fine until I attach cable [ 0 Answers ]

42" Craftsman mower. I can move the idler pulley easily, the cable moves fine (new) but when I attach the cable it won't pull the idler pulley. I don't see any visible reason for this. Any ideas?

Can you put brass cable glands on Aluminimum armour cable [ 1 Answers ]

Can you put brass cable glands on Aluminimum armour cable

Is THHN and THWN wire rated for cable tray use? If not what wire should be used? [ 6 Answers ]

Is THHN and THWN wire rated for cable tray use? If not what wire should be used in cable tray in utility chase for apartment building?

Shared neutral and sleeved cable questions? [ 4 Answers ]

Hey guys, I had a county inspector give me a two different items he had a gripe with and they are driving me crazy! Can anybody please back me up or help me out on these things? 1. I ran a 12/3 to a two gang kitchen counter outlet box- used the black for the left Gfci and the red for the...


View more questions Search