    Burners shut off during the heat cycle
    I have an older Tempstar gas forced furnace. The cycle starts up fine and about 3 minutes into it the burners shut off but the blower keeps running. The burner shuts off after the switch makes the upper temp limit like it is supposed to. I have replace the rotary temp switch twice. After I change the switch it worked fine for the rest of the season but the next season it starts all over again. The rotary switch is a Honeywell.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #2

    Nov 21, 2014, 12:27 PM
    What do you have the switch set at? Does the switch have 2 settings? You might have an air flow problem, pull the filter out and see if it does it again.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Short heat cycle and furnace won't shut off [ 1 Answers ]

I have a Luxaire Deluxe High efficiency furnace model 3 PBNU LD12N080B. We bought the house 2 years ago and all has been fine. We noticed just recently that the blower seams to be running all of the time but the furnace only comes on for a short time and never gets up to what is set on the...

Burners come on and shut off after 3 seconds. [ 4 Answers ]

I have a Tempstar NTGM075EGA3 furnace, about 7 years old, when thermostat calls for heat the igniter comes on, pilot lights, and burners come on for about 3 seconds and go out. Pilot stays on, blower comes on and stays on. If I turn furnace off at thermostat and let blower shut off, most times it...

Hunter 44155C Wiring - A/C turns on during heat cycle or heat will not shut off [ 0 Answers ]

Trying this again with the correct thermostat specs. Sorry, guys! It's a Hunter 44155C and the wires I have going into it are: White - W/B Red - Rh Green - G Yellow - Y1 Jumper from Rh-Rc

Burners cycle [ 4 Answers ]

I have a Weather King furnace and a White-Rodgers thermostat. Occasionally, the burners will cycle and the next time it would work fine. When it does malfunction, the exciter fan starts, about 30 seconds later the burners will ignite, but they go out before the fan motor starts. The burners...

Carrier split - heat burners cycle on and off [ 7 Answers ]

Carrier split unit in heat mode appears to basically operate OK. Once the pilot is lit and the burners come on, the pilot remains lit but the burners will intermittently cycle on and off. This appears to sometimes delay the blower from turning on. Once the blower turns on, it heats to the set temp...


View more questions Search