-   -   Burners shut off during the heat cycle (https://www.askmehelpdesk.com/showthread.php?t=804920)

  • Nov 21, 2014, 11:58 AM
    PolCat
    Burners shut off during the heat cycle
    I have an older Tempstar gas forced furnace. The cycle starts up fine and about 3 minutes into it the burners shut off but the blower keeps running. The burner shuts off after the switch makes the upper temp limit like it is supposed to. I have replace the rotary temp switch twice. After I change the switch it worked fine for the rest of the season but the next season it starts all over again. The rotary switch is a Honeywell.
  • Nov 21, 2014, 12:27 PM
    bitters
    What do you have the switch set at? Does the switch have 2 settings? You might have an air flow problem, pull the filter out and see if it does it again.