    dlsteimel's Avatar
    dlsteimel Posts: 2, Reputation: 1
    New Member
     
    #1

    Nov 1, 2014, 01:32 PM
    Furnace nugk100dh08. Blower trouble during heat cycle
    I have a furnace with model number nugk100dh08. When I turn the thermostat to heat the exhaust fan turns on and the burners light and stay on. The blower never turns on and the system shuts off after a few min. When turned on manually the blower will start up and stay running but not automatically during the heating cycle. I have tried multiple thermostats.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #2

    Nov 1, 2014, 03:11 PM
    The furnace is going off on high limit, not good for the heat exchanger. I can't find a wiring diagram for that furnace. Can you post a pic of the diagram?
    dlsteimel's Avatar
    dlsteimel Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 1, 2014, 03:43 PM
    The wiring diagram is at the link below on page 84. http://icpindexing.toddsit.com/docum...20PART%202.pdf I think I might have found the problem. My system relay, terminal number 1 is broken and loose in the housing of the relay. I think by looking at the wiring diagram that this would cause my issue that I am seeing?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Nov 1, 2014, 06:07 PM
    The system relay certainly sounds like a good place to start but I couldn't tell how that would effect the fan only in the heat mode. When the fan should be on, check across Brown & Yellow on the fan relay. If you get voltage that relay is open when it should be closed. If you get no voltage across Br/Y, check each side to ground or neutral.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Forced Air Furnace Blower Turns On and Off During Heat Cycle [ 0 Answers ]

Hello! I have a Lennox furnace that is approximately 10 years old. When the thermostat calls for heat, the ignitor lights and after a few seconds, a flame ignites across. After a few more seconds the blower comes on. However, after a few more seconds the blower turns off. The blower...

Our furnace blower continues to blow - cold air - after a heat cycle - help? [ 5 Answers ]

We have replaced the filters and the limit control. Didn't help.

No Heat Cycle, Purge blower motor on continuosly [ 1 Answers ]

Hi. I hope someone could help me. I have a York Stellar furnace and I am having a strange problem. The air conditioning has worked well all summer. However, when I turned on the heat the draft inducing purge motor comes on and stays on. The heating cycle does not continue beyond that. ...

Furnace stuck in the BLOWER CYCLE? [ 2 Answers ]

I have an older Reclaimer 80 furnace, it is stuck with the blower on, and the burners or not igniting, is there a way to reset the system? - I have shut power off for a couple hours and it starts back up right were it left off. Also I can't shut it down at the thermostat, that has no effect on the...

Heat pump blower does not cycle off. [ 4 Answers ]

My problem I believe is with the blower control on a heat pump. With the thermostat in COOL or AUTO, the outdoor unit stops as expected when the temperature setpoint is reached. But the blower does not stop running. It continues to run as if it's in a manual run control. If the breaker to...


View more questions Search