    Furnace stuck in the BLOWER CYCLE?
    I have an older Reclaimer 80 furnace, it is stuck with the blower on, and the burners or not igniting, is there a way to reset the system? - I have shut power off for a couple hours and it starts back up right were it left off. Also I can't shut it down at the thermostat, that has no effect on the system at this point at all.

    Thanks
    Bowser
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jan 11, 2008, 01:30 PM
    This is a normal failure mode for older furnaces. The fan relay sticks closed. How difficult and expensive depends on the furnace. It's not the only failure mode with the same symptom, though.
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #3

    Jan 12, 2008, 07:03 AM
    You have a safety open-common for older systems to lock out the burner and turn on the blower.

    Try this first... change your filter. Then look for a reset (little switch with 2 wires and a button between the wires). Push the resets-all of them-AND PAY ATTENTION TO THE ONE THAT GOES *click*. Start the furnace, and observe the flame. If the flame is nice and quiet without the blower, but flickers, dances, or goes apes**t when the blower comes on, shut it down and start shopping for a new furnace, as the heat exchanger is breached or cracked and there is no cost effective cure.

    If that didn't work, check the insertion limit-it's on the inside wall facing you-a little brown square about 2" across with 2 wires. Check for 24 volts between the two with the wires on and the furnace calling for heat. If you get 24 volts, the limit is open and you need replacement as well as finding out why it tripped (usually a packed filter). They are constructed to be "auto resetting" but many times after cycling on the limit they will fail and not reset.

    The reason you want to know which one clicked is that this will help in determining where the problem lies. If it's on the manifold for the burners or in the burner compartment, then you have a blocked vent/chimney or a breached heat exchanger. If it's the insertion limit, again a bad heat exchanger or a packed filter (most common).

    If that doesn't work...

    Contact a professional for this one. It could be something as simple as a clogged filter or as disastrous as a breached heat exchanger.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gas valve will not open on intertherm furnace blower is stuck [ 4 Answers ]

Intertherm furnace pilot is lit but burner will not I have 24 volts at valve

Stuck blower relay in furnace [ 1 Answers ]

How do I fix a stuck blower relay in my furnace or air handler?

Heat pump blower does not cycle off. [ 4 Answers ]

My problem I believe is with the blower control on a heat pump. With the thermostat in COOL or AUTO, the outdoor unit stops as expected when the temperature setpoint is reached. But the blower does not stop running. It continues to run as if it's in a manual run control. If the breaker to...

Whirlpool washer gets stuck before spin cycle [ 2 Answers ]

My Whirlpool model LST7233AQO gets stuck before it goes to the spin cycle. It doesn't happen every time, but it's happening more and more. For a while, I was able to get it to continue by depressing the lid switch by sticking a spoon handle in the slot where the lid tab goes in. Now, even that...

Craftsman 2 cycle 230 mph leaf blower [ 4 Answers ]

I accidentally used regular Castrol 2 cycle motor oil (instead of craftsman synthetic) and now the engine is seized. What do I have to do to repair the engine? The manual states to only use synthetic so I assume Sears will not repair this unit as it is only 4 months old.


View more questions Search