    Isolated Neutral Buss Bar
    I had my electrical service upgraded to 200 AMP service because I was going to remodel my kitchen and add a new washroom to the house. My new breaker sub-panel has a 24 circuit capacity but the Isolated Neutral Buss Bar has only enough lugs (lugs/screws?) for 12 circuits. I was able to locate a buss bar with 21 lugs but the screws are green. My question is, can an isolated neutral buss bar have green screws and still pass inspection? I have another question but I'll post it separately. Thanks in advance. Rob
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Jul 24, 2014, 06:14 AM
    If it has green screws, the inspector will call it a grounding bar, and therefore not isolated. Have you contacted the manufacturer?
    rgrobrod's Avatar
    rgrobrod Posts: 7, Reputation: 1
    New Member
     
    #3

    Jul 24, 2014, 07:48 AM
    Actually, I went on the manufacturer's website and could not find a buss bar with the neutral colored screws so I looked around here locally and found the one that I now have. Thanks Missouri Bound, you've answered my question. Either, I'll have to find some neutral screws or I'll have to continue looking for the proper Buss. Thanks, again... Rob
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jul 24, 2014, 08:57 AM
    Time out.

    If this is your main service panelboard than Neutral and the Ground buss are electrically bonded together. This is the only location where Neutral and Ground can be joined.
    rgrobrod's Avatar
    rgrobrod Posts: 7, Reputation: 1
    New Member
     
    #5

    Jul 24, 2014, 09:16 AM
    @donf

    Don, thanks for your response. No, it's actually a sub-panel. The problem that I have is that this breaker box is a 24 circuit box but came equipped with a 12 circuit isolated neutral buss bar. With the kitchen and washroom remodel that I'm doing, I've run out of spaces on the INBB to terminate the neutral wires for the new circuits that I'm putting in. I guess I'll just have to shop around to see if I can find one here locally. Thanks much for your help... Rob.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Buss bar [ 14 Answers ]

When adding a neutral/grounding buss bar to the main panel how do you connect to the existing bar. I was told at home depot to just butt them edge to edge.

Do single pole breakers hook black to breaker and neutral & grd to bonded neutral bar [ 6 Answers ]

I have an Eaton Cutler-Hammer meter/breaker box. (MB816B200BTS-FLCH) I want to run a 20 amp circuit (underground wire) from this box through existing underground conduit to a receptacle for a dishwasher. This run would be app. 15' to 20' and from my main house panel it would be 40' to 50'. All...

Netural buss bar grounding [ 4 Answers ]

My nephew owens a small cabin in the woods w. no electrical service. He is using a generater in the daytime and a battery/ inverter set up at night. I have installed of course a dpdt transfer switch to switch between the two sources. Im going to put one small branch circuit in the cabin which will...

What happen if you connect some grounds and neutral to the neutral bus bar and the do [ 1 Answers ]

The same conect some grounds and neutrals to the ground bus bar just using whichever bus bar is closest to the breaker so the wires don't have to travel all around the breaker box is that OK and safe to connect wires like that thank you

How to make a breaker tight on the buss bar [ 4 Answers ]

Please tell me how to make a breaker fit tight on the buss bar?


View more questions Search