    What type of cable do I need ser/ sur for 200amp service cable
    I know I need 4/o alu for 200 amp but do I use ser or sur?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jul 14, 2014, 03:22 PM
    There is no SUR, it's SEU, and it depends on what the service is for.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Jul 14, 2014, 03:27 PM
    SUR?? If entrance use SEU, If going from a main panel to a sub panel use SER. SEU does not have a ground wire, 2 hots and a bare neutral. SER has 2 hots, a shielded neutral and a ground

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size ser cable for 100 amp service [ 15 Answers ]

What gauge al ser do I need to run from a 9000 watt stand by gen to a 200 amp auto transfer switch and is this all the wireing that runs from gen to service panel in house.

200 amp service 4/0 ser cable in 2" conduit? [ 1 Answers ]

What should I run from my disconnect switch to my panel box inside for my 200 amp service. I have 2" PVC ran from the disconnect to the panel. I thought about using 4/0 SER but then read somewhere that you are not suppose to put it in conduit because of possible temp problems? Is this correct or...

SER service cable [ 3 Answers ]

Hello, My service to my house is 200 amps and terminates on the side of my house with a service disconnect located next to the meter... breaker style. This service feeds a sub panel that is where all my circuits terminate. It currently is fed through PVC conduit with Aluminum conductors. I want...

Residential Service Cable Type [ 11 Answers ]

Once again, a res. Question by a comm. Electrician. I have a new project relocating a meter service. The new meter will be about 25 feet from the 200A panelbox location instead of back to back. I'll wire in a 200A 2 pole breaker at the meter location as per 10 foot tap rule, and run new cable to...

Securing SER cable at outdoor service switch [ 1 Answers ]

What options for securing 4/0 SER at the outdoor service entrance breaker box - Frame house, service switch located on exterior on siding - thanks