What else gets damaged besides the elements on a water heater?
We just got bought a BRAND NEW water heater and apparently we didn't install it properly and burned out the elements, but we've replaced the elements and it doesn't want to heat up the water still. What could still be damaged?
|
|
 |
Uber Member
|
|
Jul 2, 2014, 10:48 AM
|
|
What did you do wrong during the installation that caused the elements to burn out? Wired it wrong or forget to turn the water on before turning on the power?
|
|
 |
Uber Member
|
|
Jul 2, 2014, 11:48 AM
|
|
Thermostats.
|
|
 |
New Member
|
|
Jul 2, 2014, 11:53 AM
|
|
Well I actually forgot to let the air out first, which in turn burnt the elements, but I've replaced the elements and its still the same. Could it be the thermostat?
|
|
 |
New Member
|
|
Jul 2, 2014, 11:56 AM
|
|
I just don't want to spend more money on something that I won't need and can't return... I don't have much to spend and I've already spent too much money on buying the damn thing. So I'm trying to figure out what could surely be wrong before I go buying another part
|
|
 |
New Member
|
|
Jul 2, 2014, 11:57 AM
|
|
How can you check if the thermostats are damaged?
|
|
 |
Uber Member
|
|
Jul 2, 2014, 12:56 PM
|
|
 Originally Posted by jrsj348
How can you check if the thermostats are damaged?
Make sure the unit is filled. Turn on the power and measure voltage across the elements. Top element heats first and then thermostat switches to bottom. Should measure 240 VAC across top terminals of element and then later 240 across the bottom. Make sure breaker-should be a double pole-is turned on.
|
|
 |
Eternal Plumber
|
|
Jul 2, 2014, 01:10 PM
|
|
When the elements burned-out did it trip the breaker? Did you push the red reset button on the thermostat? What have you done so far? Do you have a AC voltmeter? This is an electrical problem. Start checking from the breaker's through the thermostats. Let us know what you find. Good luck, Tom
|
|
 |
New Member
|
|
Jul 2, 2014, 01:26 PM
|
|
I don't own an AC voltmeter is there any other way to check if the thermostat is broken, and no the breaker didn't trip, and I've only switched out the elements pretty much.
|
|
 |
Full Member
|
|
Jul 2, 2014, 01:34 PM
|
|
Make sure you're comfortable, and confident about using a volt meter before you begin measuring voltage anywhere.
You can get a 240 volt reading at the upper element terminals, and still have a bad element. I prefer to test the upper ( or lower ) element by disconnecting ( safely ) the wire from one of the element terminals, and then checking for voltage at that terminal, and to ground; you will register 120 volts through the element as long as it is good, and, there is voltage leading there through the t-stat.
|
|
 |
New Member
|
|
Jul 2, 2014, 01:47 PM
|
|
Either way if the elements aren't burnt again then it must be the thermostat, no? Because I have absolutely no idea how to use an AC voltmeter, and don't want to mess with the water heater wiring unless I ABSOLUTELY have to.
FYI though the reason i burnt the elements was because i didnt air it out enough.
|
|
 |
Eternal Plumber
|
|
Jul 2, 2014, 01:49 PM
|
|
Did you push the red reset button located on the upper thermostat ? Tom
|
|
 |
New Member
|
|
Jul 2, 2014, 01:51 PM
|
|
Yes I did that after I installed the new elements and filled it with water, i pressed it
|
|
 |
Eternal Plumber
|
|
Jul 2, 2014, 02:20 PM
|
|
If the breaker is okay then the next thing I would be replacing would be the thermostat. Replace wire for wire and let us know if that works for you. Good luck, Tom
|
|
 |
Home Improvement & Construction Expert
|
|
Jul 2, 2014, 02:53 PM
|
|
This may or may not help.
https://www.askmehelpdesk.com/attach...thermostat.jpg
You should also note that the red reset button is a thermal over temperature switch. It is not an electrical circuit breaker.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Water heater mixed elements
[ 2 Answers ]
I have a 6 year old electric water heater. 50 gallons It is rated at 4500 watts. I had to replace the lower element. I went to home depot and got a 4500 watt element. When I pulled the old element it was only a 3500 watt. I replaced it with the 4500 watt I got from home depot and filled the tank...
Wiring both elements together on a hot water heater?
[ 2 Answers ]
I am using a hot water heater to heat the in floor heat in my shop, I am having trouble getting the water hot enough, I have been told to wire the heater so both elements come on at the same time,, I have 10-3 wire and a 40 amp. Breaker,, Two 3000 watt elements and 40 gallons of water. How do I...
Can I use 3500 watt water heater elements to replace 3800 watts?
[ 3 Answers ]
I haven't actually pulled the elements yet but the tag on the water heater shows elements rated at 3800 watts. The ones readily available at the local big box are even numbered, 3500, 4500,5500.
Can I use the 3500 watt rated elements to replace elements in this water heater?
220 v hot water heater elements problems