    Wiring both elements together on a hot water heater?
    I am using a hot water heater to heat the in floor heat in my shop, I am having trouble getting the water hot enough, I have been told to wire the heater so both elements come on at the same time,, I have 10-3 wire and a 40 amp. Breaker,, Two 3000 watt elements and 40 gallons of water. How do I wire the heater so they both come on at the same time?

    Thx.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 10, 2010, 06:43 AM

    First off, #10 wire is too small to be on a 40 amp breaker. This is not a safe condition, and should be a maximum of a 30 amp CB.

    Wiring a unit with 6000 watts at 240 volts will total 25 amps.

    A 30 amp circuit for a water heater is to be derated by 80%, which is 24 amps, so that is not allowed.

    You need to change the wiring to #8 copper for a 40 amp circuit to continue on with your plan.

    Next you need to check the rating of the thermostat in the heater to see if it can handle 6000 watts.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Dec 10, 2010, 03:43 PM

    I'm curious. How large is the shop? What is the estimated btu's needed for this shop? How large is the hot water heater circuit? In most circumstances if you are sized properly, the water heater will keep up under two conditions: It's sized properly and you don't turn it off when unoccupied. Are you using baseboard or in floor radiant?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a hot water heater [ 4 Answers ]

I'm installing a hot water heater at the cottage, there is a 240 circuit already in place that was wired for a dryer - so it has black, red, white and bare copper. The water heater has the standard black, red and green for 240v. I know the dryer wire black and red are hot and on the water heater...

Hot water heater wiring [ 3 Answers ]

I have a 30 amp hot water heater I want to put a switch on it how do I conect the wires to th switch? Ron

Wiring up a hot water heater [ 3 Answers ]

How do you wire up a hot water heater if the wires from the water heater are red and black and the wires from the wall are black and white?

220 v hot water heater elements problems [ 1 Answers ]

I have a standard run of the mill 40 gallon 220v 2-element electric hot water heater that is now giving me all kinds of problems. It is only 8 yrs old and has worked great. There are only 2 people in this householld to use this water heater. In the past 14 months, I have developed dark water...

Wiring a hot water heater [ 1 Answers ]

I am wanting to wire a new hot water heater that is 220. Do you have a diagram of a subpanel that I could use? What do I look for on the subpanel, what wire do I use, and how does this wiring differ from 110? LK


View more questions Search