    I have a goodman a49-20 heat pump. Outside unit and oustide fan are not running.
    I have a goodman a49-20 heat pump. Outside unit and oustide fan are not running. Have replaced sequencer on inside unit. Also replaced the defrost board and contactor. Capacitor is new too. Any ideas?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Feb 7, 2014, 08:03 PM
    Does the contactor pull in? If not :
    When measuring at the defrost board, do you get 24 volts between Y & C, and O & C?

    If the contactor is pulling in: What voltage do you have across the incoming line voltage terminals on the contactor? How about on the out going terminals?
    dknix187's Avatar
    dknix187 Posts: 5, Reputation: 1
    New Member
     
    #3

    Feb 8, 2014, 02:23 PM
    Thanks for the quick response. I don't have anything to measure the voltage, so I am not sure.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Feb 8, 2014, 06:49 PM
    Can you tell if the contactor is pulling in?
    dknix187's Avatar
    dknix187 Posts: 5, Reputation: 1
    New Member
     
    #5

    Feb 9, 2014, 06:28 AM
    I don't think so. After I replaced it, it does not seem to be doing anything. I also replaced the outside circuit breaker yesterday. The unit does not seem to be getting any power.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #6

    Feb 9, 2014, 09:51 AM
    You need a voltmeter to do any testing & troubleshooting. We can throw parts at this thing all day long & spend a whole bunch of money only to find out there was a broken wire in the low voltage system.
    dknix187's Avatar
    dknix187 Posts: 5, Reputation: 1
    New Member
     
    #7

    Feb 11, 2014, 05:11 PM
    Yes, you are right. I need to get one. I had someone check last night and I an getting power to the outside unit. The Freon was completely out meaning I have a big leak. We're going to try and find it, but if it is in the air handler coil, I will probably need to end up replacing the whole unit rather than spending a bunch on a 15 year old unit. I appreciate your help and advise.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #8

    Feb 11, 2014, 08:46 PM
    With a 15 year old heat pump, I wouldn't waste the time trying to find a leak which, if in one of the coils, in all probability isn't going to be repairable anyway.
    The new R410A heat pumps do a far better job of heating than did the R22 units.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Outside unit on Goodman heat pump not running [ 0 Answers ]

I have a 15 year old Goodman heat pump. Neither the outside unit or outside fan motor are running. The inside blower will kick on and run for a few minutes, just circulating air. After about 5 minutes, the aux heat kicks on and warms the house. I have checked the circuit breakers and none are...

I have a Goodman heat pump, I think about 5 ton unit. The fan keeps stopping [ 2 Answers ]

The fan will stop after aprox 5 - 10 minutes. The motor was replaced, same issue. Then the tech bypassed the defrost relay, same issue. Then he wired straight to the contactor with same issue.

My Goodman heat pump, model GSH130361AD, in heat mode outside unit does not start up. [ 10 Answers ]

Goodman heat pump, model GSH130361AD, Goodman AEPF series Air Handler, and a Honeywell T8411R t-stat. After wiring and setting everything up, the A/C works very good. In heat mode the aux heat comes on but the outside unit does not start up. Emergency heat works well too. The units are used...

Heat Pump A/C unit not pumping cold air, but fan is running [ 13 Answers ]

Hello everyone, first time poster so please bare with me. We have 2 units, the main floor unit stopped working this week. By "stop working" I mean that the unit will not blow cold air. The fan appears to be blowing because air is coming out of the vents and the air is room temperature. We turned...

Goodman Heat Pump compressor keeps running [ 1 Answers ]

In Heat mode, compressor outside continues to run even when the blower inside is not running. If I switch the thermostat switch from Heat to off, the compressor stops but sometimes kicks back on, even with the thermostat switch still in the off position. At this point, I have to cut power via the...


View more questions Search