  • Feb 7, 2014, 01:25 PM
    dknix187
    I have a goodman a49-20 heat pump. Outside unit and oustide fan are not running.
    I have a goodman a49-20 heat pump. Outside unit and oustide fan are not running. Have replaced sequencer on inside unit. Also replaced the defrost board and contactor. Capacitor is new too. Any ideas?
  • Feb 7, 2014, 08:03 PM
    Grady White
    Does the contactor pull in? If not :
    When measuring at the defrost board, do you get 24 volts between Y & C, and O & C?

    If the contactor is pulling in: What voltage do you have across the incoming line voltage terminals on the contactor? How about on the out going terminals?
  • Feb 8, 2014, 02:23 PM
    dknix187
    Thanks for the quick response. I don't have anything to measure the voltage, so I am not sure.
  • Feb 8, 2014, 06:49 PM
    Grady White
    Can you tell if the contactor is pulling in?
  • Feb 9, 2014, 06:28 AM
    dknix187
    I don't think so. After I replaced it, it does not seem to be doing anything. I also replaced the outside circuit breaker yesterday. The unit does not seem to be getting any power.
  • Feb 9, 2014, 09:51 AM
    Grady White
    You need a voltmeter to do any testing & troubleshooting. We can throw parts at this thing all day long & spend a whole bunch of money only to find out there was a broken wire in the low voltage system.
  • Feb 11, 2014, 05:11 PM
    dknix187
    Yes, you are right. I need to get one. I had someone check last night and I an getting power to the outside unit. The Freon was completely out meaning I have a big leak. We're going to try and find it, but if it is in the air handler coil, I will probably need to end up replacing the whole unit rather than spending a bunch on a 15 year old unit. I appreciate your help and advise.
  • Feb 11, 2014, 08:46 PM
    Grady White
    With a 15 year old heat pump, I wouldn't waste the time trying to find a leak which, if in one of the coils, in all probability isn't going to be repairable anyway.
    The new R410A heat pumps do a far better job of heating than did the R22 units.