        Can I put a under counter refrigerator and tankless water heater(1800 watts) on a 20amp breaker?
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Nov 8, 2013, 10:31 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        What is the wire gauge? Will that be the only two appliances, no outlets or lights?
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Improvement & Construction Expert |  | 
 
                  
                      Nov 9, 2013, 05:41 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        What is amperage of refrigerator?  Eighteen hundred (1800) watts is 15 amps.
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Nov 9, 2013, 10:54 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        By code, no single cord and plug connected appliance can be more than 80% of a multiple outlet branch circuit.  On a 20 amp circuit that shakes out to 16 amps.
 Water heaters are considered to be continuous use so, (1800 / 120) * 1.25 = Amperage
 1800/120 = 15 Amps.  15 * 1.25 = 18.75 Amps.  So basically, the water heater is going to suck up 19 amps.
 
 So, the answer is no.  Place the water heater on it's own dedicated circuit.  Use #12 AWG Copper for the conductors and protect the circuit with a 20 amp breaker.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Electrical & Lighting Expert |  | 
 
                  
                      Nov 9, 2013, 04:28 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Actually, an insta-hot water heater is fixed in place, so it cannot be more than 50% of the circuit. 
 Also, an insta-hot water heater is not considered a continuous load. That only applies to storage type water heaters.
 
 Either way, no, this water heater cannot be on with another appliance or counter circuit.
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Nov 11, 2013, 07:40 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Stan,
 So the term "fixed-in-place" applies to the equipment, not the connection type as in hardwired?  A fixed in place appliance can be either cord & plug connected or hardwired?
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Ultra Member |  | 
 
                  
                      Nov 14, 2013, 05:24 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by stanfortyman   Actually, an insta-hot water heater is fixed in place, so it cannot be more than 50% of the circuit.  Stan, where is this in the book?
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Nov 14, 2013, 06:38 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        2011 - nec 210.23(a)(2)
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Ultra Member |  | 
 
                  
                      Nov 14, 2013, 08:22 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Don,Thanks! I was lost in different chapter...
 |  
    |  |  
 
 
 
  