    Goodman air handler 24 vac common wire terminal
    Have a Goodman AWUF300816BA Air Handler, Single Cool, Heat Strip (No Heat Pump) looking for wiring diagram for 5 wire programmable thermostat. Specifically can't locate on Air Handler 24 VAC Common wire terminal location.
    dewey066's Avatar
    dewey066 Posts: 49, Reputation: 1
    Junior Member
     
    #2

    Sep 16, 2013, 02:49 AM
    There isn't always a low-voltage wiring diagram.

    Typical terminal designations are:

    C - Common of 24V Transformer
    R- "High Side" of 24V Transformer
    W - Energizes Heat Relay
    Y - Energizes Cooling Relay (contactor in condenser)
    G - Energizes Fan Relay

    It may be necessary to trace out and see where the wires actually go. Typically a 5-wire cable will run to the thermostat, and then you will have two wires going to the relays (Common and then W, Y and G depending on which relay it is - this gives you the 24V to energize the relay).

    All a thermostat does is connect R to W for heat, connect R to G for fan, and R to Y for cooling (cooling in "Auto" also connects G to R).

    Hope this helps.
    DTampaBayD's Avatar
    DTampaBayD Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 20, 2013, 09:47 AM
    Thank you for your help. I don't have a problem with the wires between air handler and old thermostat. However, the new Honeywell Programmable WiFi Thermostat requires a 24 VAC common wire that was not used in the old thermostat.

    What I don't know is where on the Goodman air handler is the "C - Common 24 vac connector to attach a wire from the thermostat? Currently, there are only 4 wires between the air handler and the old thermostat; Green, Yellow, Red, White.

    I don't see a connector available for the black/blue C Common 24 vac wire on the air handler so I don't know where to connect the wire. I had hoped there would be a 5th wire, black/blue connected from the air handler to the 24 vac location and not connected to the old thermostat. At least I could locate the wire and use it. I had to run a new thermostat wire with 2 conductors and only use one of them whenever I learn where to connect it on the air handler.

    Thank you.
    dewey066's Avatar
    dewey066 Posts: 49, Reputation: 1
    Junior Member
     
    #4

    Sep 23, 2013, 04:01 AM
    Okay, as long as you have a wire, go to the air handler where all the connections are for the thermostat.

    A 24 Volt transformer has either two screw-terminals on it, or a pair of low-voltage wires coming off it. If you trace where the "R" from the thermostat goes to that will lead you to the transformer. (The R may come back to the airhandler to a terminal strip, a circuit board, relay, etc).

    The "R" is the "High-Side" of the low voltage transformer. Like I said there will either be two terminals (screws) or two wires coming off the low voltage side, and two or more wires that connect to high-voltage side of the transformer (the power going into it). So whatever wire comes from the R on thermostat keep tracing it back until you find a "heavy" metal transformer. The Low-voltage wire that the R is NOT connected to is your "C" or common. The common wire wire will be connected to the contractor in the outside condenser for A/C ( the other wire is the "y"), and to the fan (blower) relay (these are usually brownish with a bunch of wires connected to the NormallyOpen or Normally Closed contacts on it - there is also a 24V coil that energized the relay and turns on the fan.

    Connect the wire you ran from this screw terminal (if it is that type), or remove the wire-nut on it and connect your wire to this. It's a good idea to shut the power off when you do this so you don't short out your transformer.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman electric air handler [ 0 Answers ]

Hi, have a goodman electric air handler with heat strips. When the power is applied from the breakers the fan and heat strips come on. The stat is off, no g or w call.

Goodman air handler schematic? [ 0 Answers ]

Schematic for heater sequencers

Thermostat for the Rheem RBHM Air handler with on demand dehumidification terminal [ 0 Answers ]

I am looking to buy the proper thermostat for a Rheem RBHM Air handler with on demand dehumitification.

Goodman aepf air handler [ 0 Answers ]

I am currently having a problem with a goodman 16 seer air handler after the system meets temperature the blower motor keeps running. I have done several things and even called goodman tech support and got no help. I want to know if it has something to do with the purple wire that comes off the...

Wiring air handler goodman A-30 [ 2 Answers ]

Trying to take goodman air handler A-30 from straight ac and convert to heat pump fan coil only has three low voltage wires how do I go about wiring?


View more questions Search