    The terminal board on my heat/ac unit has letters C,W, R, G, Y.
    I have a RUUD heat & ac unit I replaced the indoor switch, indoor run compactor, and inside blower motor. The wires do not match the letter on the terminal board, There are two set s of wires, both has only 4 wire and the color matches B, Y.R. G. what do I do. The inside motor comes on ,but the outside does not.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #2

    Aug 8, 2013, 10:26 PM
    You should not have changed any low voltage wiring just to change a fan motor. What did you find that required you to change the low voltage wiring? It should have been a very simple and easy change out of the fan motor where nothing else was affected. If the outside unit won't run you are not energizing Y and C to the outside unit. "B" is probably Common which is the other side of transformer opposite "R." R is switched through the t-stat to go to Y for outside unit along with Common. It's not rocket science. Here are some diagrams: https://dl.dropboxusercontent.com/u/...20Diagrams.zip
    https://dl.dropboxusercontent.com/u/...e%20Manual.pdf
    You need to use a meter to check it and to know how to wire it. If you do not have one do not work on it. It is never done without a meter to check what you have.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to wire in a thermostat on a Bryant furnace, on the control board I have terminal [ 1 Answers ]

How to wire in a thermostat on a Bryant furnace, on the control board I have terminals W, Y, R, C for 24 volt common & G and on the thermostat I have terminals W, Y, R, G. Thank you Tom.

VAV terminal unit working [ 1 Answers ]

Can someone please explain the working of a pressure independent VAV terminal unit that is normally installed in a room which is being supplied air through central constant air volume ducting system. How it is controlled through thermostat, is it CFM that we adjust at the thermostat or the...

Powering the G terminal on my furnace control board [ 1 Answers ]

Hi! My furnace's control board recently blew and the repair guy replaced it with a different kind. Aparently the new board requires a wire from the thermostat to the G terminal to work the A/C fan, and the old one didn't. The repair guy would need to make another trip for this repair. I am...


View more questions Search