    Home circuit
    Hello, we have a 50 Amp 240 VAC circuit with a single outlet in the garage area pulled there by previous owner for an electric dryer. There are no plans on our part on installing an electric dryer or any other 240 VAC appliances in that area.

    My question is if it is acceptable to use one of the poles of this never used 240 VAC circuit for powering 120 VAC devices and keeping the other pole isolated? Would it be just a matter of installing a split-circuit receptacle, i.e. using both hot wires?

    Thanks, h.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #2

    Jul 13, 2013, 09:58 PM
    Would this scheme work? First, break brass connecting fin at the "hot" side of receptacle; then connect the red wire to one brass "hot" terminal and the black wire to the other; then connect the "neutral" wire to one of the silver terminals.

    The top and bottom halves of the outlet will be powered by different hot wires with 120 VAC. The "neutral" wire will be shared, which is acceptable because the "red" and "black" current would be of opposite phases.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Jul 13, 2013, 10:10 PM
    How do you plan to connect a wire rated for 50 amps to a 15 or 20 amp outlet. If you put a 12 or 14 on for a pigtail you would need to change the breaker. Why not put in a small subpanel, leave the 50 amp breaker and you could have 240 and 120 VAC circuits.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #4

    Jul 13, 2013, 10:14 PM
    I still haven't been able to locate the main shut-off switch that powers off the main panel: there is no visible switch at the roof where the service enters the house or around the panel. I have been doing some electrical work switching off individual breakers rather than main power.

    With the breaker for this particular circuit off, when I touched the "neutral" wire with the "ground" wire in one of the kitchen outlets, there was always a small spark between them. In contrast, touching the "hot" wire with the "ground" does nothing. My power tester shows no voltage in any of the wires. Is this something to expect? What is the explanation for this? Is this because the "neutral" wire in the outlet, even with the breaker off, is still continuous with the city service "neutral" (with some non-zero potential), and it is the "hot" wire that is interrupted by the breaker?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #5

    Jul 13, 2013, 10:18 PM
    50 Amp 240 VAC
    No, a 240V circuit has no neutral.

    With the breaker for this particular circuit off, when I touched the "neutral" wire with the "ground" wire in one of the kitchen outlets
    What does a circuit in the kitchen have to do with a 240V circuit to the garage?

    when I touched the "neutral" wire with the "ground" wire in one of the kitchen outlets, there was always a small spark between them
    That indicates an open neutral on that circuit.

    is the "hot" wire that is interrupted by the breaker?
    Yes.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #6

    Jul 13, 2013, 10:28 PM
    Quote Originally Posted by hkstroud View Post
    No, a 240V circuit has no neutral.
    Do you mean the current goes through the water pipes to the ground and doesn't return to the city line? I thought that I have three wires: -120VAC, +120VAC and the "neutral" "returning" wire. Or are you talking about home service in Europe?

    Those are two different circuits. I put two questions in the same thread.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Jul 14, 2013, 02:47 AM
    You know just enough to be really dangerous. :) I suspect that if the receptacle is up high on the wall it was for a welding unit and not a dryer. Also, for this type of circuit testing, use a Multi-meter and check for 240 Vac between both hot pole on the receptacle.

    If you have zero volts across the hot poles, then the breaker may be off or have already been removed. If it has been removed already, then pull the entire circuit.

    There are two 240 Vac receptacle configurations. A Three wire, 2 hot conductors and one Neutral / Ground" wire. The four wire configuration has 2 hot conductors, a Neutral conductor and a Ground conductor.

    The three wire configuration is no longer an acceptable configuration. It has been replaced with the four wire. The 3 wire configuration came about as a method to save on the use of copper during WW II. The problem with this configuration is that "Neutral", which is a current carrying conductor is connected to the frame ground of the appliance and the Ground is then used to transfer the return current back through the circuit to the panel board.

    What you are going to have to do is trace the cable from the receptacle to the panel board and to the breaker. The breaker should be fairly easy to find. It will be a double pole breaker 40 or 50 amp breaker. Once you have identified the breaker, turn it off and then remove the breaker and the entire circuit .
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #8

    Jul 14, 2013, 05:17 AM
    Those are two different circuits. I put two questions in the same thread.
    OK, while that was not very smart thing to do, you got two answers.

    1. You said you have a 240V circuit to the garage.
    If you have a 240V circuit you have no neutral.

    2. If you get a spark when connecting a neutral to a ground wire, you probably have an interrupted neutral.

    Not smart present two different problems in one thread because it is difficult to convey all the aspects of one problem to someone remotely over the internet, much less two. Only creates confusion. If you are going to do that, state "I have a second problem" so that everyone knows you are talking about a different problem.

    Don is correct that if this is a 50 amp circuit it is most likely for something other than a dryer. Dryer circuits are most often 30 amps.

    If your garage circuit has 3 wires, two hots (black and white and ground) you have a 240V circuit. If it has 4 wires (black, red, white and ground) you have a 240/210V circuit. How many holes or slots does the receptical in the garage have, 3 or 4?
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #9

    Jul 14, 2013, 11:11 PM
    Quote Originally Posted by donf View Post
    You know just enough to be really dangerous. :)
    ...
    ...
    ...

    What you are going to have to do is trace the cable from the receptacle to the panel board and to the breaker. The breaker should be fairly easy to find. It will be a double pole breaker 40 or 50 amp breaker. Once you have identified the breaker, turn it off and then remove the breaker and the entire circuit .
    Thanks for the answer. The receptacle is 30-40 in. above the floor. The breaker is off, because I turned it off. I have assumed that this 240 VAC circuit is otherwise in good shape and ready to use. It runs all the way from the main panel (the panel is without any sign of the main shut-off switch) in a metal sheath in the crawl space.

    The outlet was made for electric dryer, I know it. This is an old house with a small 100 A main panel, and I am reluctant to remove a ready-to-use circuit.

    Maybe the best solution is to substitute a 20 A breaker for the old 50 A and split the outlet, one receptacle per "hot" wire -- this way, I will have two extra 20 A receptacles.

    Yes, there are only three wires, i.e. there is no ground. But the circuits like this are still legal, i.e. one doesn't have to pull new 4-wire lines.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #10

    Jul 15, 2013, 06:21 AM
    Thanks for the response. It seems as if you are set on doing it your way.

    If this is a true 240 Vac circuit, you will only have two hot legs and ground. That tells you that you have no Neutral (White). Without a Neutral, you cannot create 120 Vac circuits.

    You cannot use the Ground wire as a Neutral.

    You would be much safer in just abandoning the existing circuit and creating two new circuits.

    Technically what you want to do is called a Multiwire circuit. Two hot wires each with their own breaker sharing the Neutral.. However, the risk here is that if you ever have a Neutral failure, you would be putting 240 Vac across each receptacle.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #11

    Jul 15, 2013, 07:56 AM
    Thanks again. Yes, putting this line to use will take some tweaking. No "neutral" means that I will have to pull one or two new lines.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #12

    Jul 15, 2013, 08:04 AM
    And when you pull these additional wires, you know they need to be in the same raceway or part of the same cable assembly?
    So, now that your pulling some new wires, why not pull the correct new circuits you wanted and leave the 50 amp circuit and outlet for the future? Do it once and do it right...
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #13

    Jul 16, 2013, 07:11 AM
    Quote Originally Posted by hfcarson View Post
    and when you pull these additional wires, you know they need to be in the same raceway or part of the same cable assembly?
    So, now that your pulling some new wires, why not pull the correct new circuits you wanted and leave the 50 amp circuit and outlet for the future? Do it once and do it right...
    Well, I will definitely leave the 50 VAC line intact for future use, i.e. when I upgrade to 200 A main board. It is a perfectly working circuit, but of not much use at this point.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Home air conditioner circuit won [ 1 Answers ]

During the night, our air conditioner on our home stopped working. The fan works fine, when I go to reset the circuit, it buzzes and kicks off.?

My home a/c unit circuit breaker keeps tripping it will not stay on what wrong? [ 1 Answers ]

My home A/C unit is 4 years old just replace the coil last year, now the same unit want cool down the temperature after a few hours running. I went to flip the circuit breaker and notice it was tripped so a tried to turn it back on it would stay, so I cut off the air conditioner for now. What could...

Connecting a new circuit to numerous home with outdated electrical systems. [ 1 Answers ]

Seeking general advice in Michigan. I am working on a sewer system for over 200 existing homes. Many of these homes are over 50 years old and I am sure there are at least a handful with substandard electrical systems. Each of these homes will need to connect a 1/2 HP, 120V pump to their...

Appliance circuit breaker or home wiring? [ 1 Answers ]

HI, I have an electrical top stove, GE, that is about 2 years old. I also have a double wall oven by Hot Point, ancient. I had both on today cooking dinner. There was a POP and both went off. The main circuit breaker on the electrical panel did not flip. Neither will turn on. Tried to flip the...

60 amp 230volt home circuit needed [ 3 Answers ]

I'm going to be running a Plasma Cutter and 230V Tig welder. The plasma cutter requires between 55-60 amps maximum. I was wondering what I need to do in order to run a 230 volt, 60 amp circuit from garage mounted circuit panel, to an external receptacle outside of my basement on a concrete...


View more questions Search