    Jul 12, 2013, 09:58 AM
    Fan in the outside unit shuts off after some time
    Hello,

    The fan in the outside unit of my Goodman airconditioner shuts off after about an hour when the thermostat is set to cooling. Here is the sequence:

    1. Switch thermostat from "Off" to "Cool"; Fan is set to "Auto"
    2. Snowflake indication shows upon thermostat, both indoor fan and outdoor unit Fan start running and cooling takes place.
    3. After some time (about an hour or so), the outdoor unit fan stops spinning, indoor unit fan continues to run for hours until switched off.
    4. Switch thermostat from "Cool" to "Off" to switch off indoor fan.

    The above cycle repeats if the thermostat is switched back to "Cool" after a few hours.

    Can someone please help.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Jul 12, 2013, 07:05 PM
    The problem could be as simple as a capacitor but most likely the condenser fan motor is in need of replacement.
    slm's Avatar
    slm Posts: 18, Reputation: 1
    New Member
     
    #3

    Jul 12, 2013, 07:41 PM
    Quote Originally Posted by Grady White View Post
    The problem could be as simple as a capacitor but most likely the condenser fan motor is in need of replacement.
    Thank you for your response Grady. The fan came on a couple times after extended periods of gap yesterday but did not work at all today evening. Are there any voltages that I can check? Is the condenser fan motor easy to replace? Can you point me to any DIY instructions?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Jul 14, 2013, 05:35 PM
    Does the compressor shut off too or just the fan? It wouldn't take long, probably just a minute or two, for the compressor to shut down after the fan shuts off.

    Rather than spending a lot of time trying to catch it in the act, I'd suggest replacing the capacitor. They are inexpensive (normally less than $20) & easy to replace.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New Lennox 5-ton unit makes a loud noise when fan shuts off [ 2 Answers ]

I have a new Lennox 5-ton outside unit, occasionally when the fan motor turns off, there is a loud bang coming from the unit. My service tech is telling me it was caused by damage from the company that replaced my roof, and I need a new unit. Is this caused by a bad motor? Or is it possible small...

Fan on condenser unit not turn all the time. [ 0 Answers ]

Sometimes the fan blades turn on outside unit and sometimes I have to turn ac off and back on. What could cause this?

Unit shuts down after 3 hrs run time [ 0 Answers ]

Replace collector due to cracks also both heat xchanges .started up system OK but after 2-3 hrs run time unit shuts down on#3 code replaced pressure switch same thing checked condensate drain good.

My trane unit only heats when the fan is on all the time [ 0 Answers ]

I have a trane 2/4 TEE3F65 with a TCONT802 Themostat. The unit will heat but only when the fan is running all the time. In the auto mode the stat calls for heat but the fan does not kick on, so I am not sure if the heat is running with no fan or nothing is running. Either way the Fan has to be...

In heat modes, unit shuts off, but circulation fan does not [ 3 Answers ]

I have a single stage heat pump and a hunter model #44360 thermostat. Put in this summer, worked fine all summer. Now that we want to use the heat, an issue has come up. The unit kicks on and heats to the desired temp. Then the unit shuts off. The fan for circulationg the air however does not....


View more questions Search