    My gas furnace is occasionally short cycles, leading to system lockout.
    Occasionlly (once or twice per week), when gas is called for, 5 of the 6 inshot burners ignite, but the 6th, containing the flame sensor will not ignite. This causes the gas to shut off and then the unit recycles sometimes igniting properly and sometime going into system lockout after 3 tries
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Feb 28, 2013, 06:46 PM
    Classic case of a dirty cross igniter bar. Many time you can blow out the burner assembly with compressed air to fix the problem. Sometimes you have to remove the burner assembly and physically clean the cross igniter bar/channel. If the compressed air doesn't do it, I would suggest having a tech in to check gas pressures, remove burner assembly, and otherwise service the furnace.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have an indicator light telling me that my gas heat system is in system lockout [ 0 Answers ]

Gas heat system shuts down before it reaches its set temperature. One single red blinking light is going on indicating that the system is in ''system lockout (retries exceeded)

My blower fan/furnace motor on my natural gas/air conditioning system short cycles? [ 1 Answers ]

This summer I had my air conditioning unit replaced after the previous one unknowingly froze up and as a result blew up. The new unit was working well after it was installed in conjunction with the natural gas furnace without issue - albeit the blower on the furnace unit distributes the cold air...

Cold gas pipes=System lockout? [ 3 Answers ]

I am having the following issues with my forced air gas furnace. It has a White Rodgers 50A55-843 board. The valve has "36E03 205" on it, along with a logo which looks like a "C" with an "A" inside of it. The majority of the time the furnace works. However some days in the morning I wake up and...

Carrier furnace short cycles [ 1 Answers ]

I have a carrier furnace and when I switch to heat on the tstat the inducer fan comes on then the burners ignite then the blower motor comes on, after about 45 seconds or so the blower motor and burners cut off but the inducer fan keeps running and this process starts again in 10 to 15 minutes with...

Short Furnace Running Cycles [ 7 Answers ]

My furnace only runs for 15-30 seconds at a time. It will kick off and then fire up 2 minutes later for about another 30-40 seconds. The desired temperature is maintained but the very short on and off cycles are very annoying. We were told it may be our thermostat so we installed a new one and we...


View more questions Search