Ask Experts Questions for FREE Help !
Ask
    Blackwing's Avatar
    Blackwing Posts: 1, Reputation: 1
    New Member
     
    #1

    Feb 15, 2013, 09:09 AM
    Shared neutral on arc fault circuit
    I have an old house we are partially rewiring. To meet the NEC we have installed arc fault breakers where required. In one bed room the circuit breaker will not remain set. I have checked the boxes and verified all of the connections and can find no problem. Could we have a shared neutral in some of the old wiring?? Would this cause the arc fault to trip?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Feb 15, 2013, 09:42 AM
    Or you could be having an Arc Fault?
    Either way, try to troubleshoot this circuit... disconnect the circuit somewhere near the middle and see if the breaker will reset. If not, continue dividing the circuit until it clears... now you will have a much better idea of where the problem is...
    Good luck...
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Feb 15, 2013, 03:10 PM
    Or you could have a neutral touching a ground somewhere.

    Why did you install the arc-faults? You do not need them on old wiring to meet NEC code. These requirements are not retroactive.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Feb 15, 2013, 09:17 PM
    Have you swapped breakers with one known to be good? Defective arc fault breakers are far from unheard of.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Arc fault circuit [ 5 Answers ]

For a bedroom with 5 recessed lights (I will use 26 watt compact fluorescence lights) 8 wall outlets, and a ceiling fan is one 20 amp circuit with an arc fault breaker sufficient, and code compliant? I had planned on two circuits, one 15 amp circuit for the lights and one 20 amp circuit for the...

Arc-Fault Circuit [ 1 Answers ]

In a commercial building, namely a fire house, with sleeping quarters, do the circuits in those rooms need to be arc fault protected.

Arc Fault Circuit [ 3 Answers ]

Hello, Only when using my portable generator, the arc fault circuit (for Master Bedroom) keeps tripping.. Do I have to do anything extra?? Details: Coleman powermate 5kw Maxa ER Plus (pm0525312.17) Using the L14-20 receptical with Floating Neutral 10/3 W/ground Bus Drop cable (35 ft) to...

Arc Fault circuit [ 2 Answers ]

I have a 3-wire home run to the panel which supplies 2 circuits. One of the circuits supplies a bedroom and I want to comply with the arc-fault breaker protection rule. Square D indicates the common neutral will cause the arc-fault to trip. Is there a solution to this? Bob

Arc Fault Circuit Interrupters [ 4 Answers ]

I realize I have to run Arc Fault Circuit Interrupters for all three of my bedrooms. I was planning on using fluorescent lights in the closets of those bedrooms. True or False, Can I run fluorescent lights on an Arc Fault Interrupter circuit?


View more questions Search