    Electrical questions and answers
    I'm replacing a 240 baseboard heater with a 240 1500 watt baseboard heater. The original one was wired with 10-3 600 wire on a 30 amp circuit. Can I replace the 10-3 600 wire with 12-3 300 wire?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Feb 12, 2013, 11:11 AM
    Clarify for us do you mean, 10-3 600 is 10 gauge, 3-conductor, 600 volts?
    And 12-3 300 is 12 gauge, 3- conductor, 300 volts?

    If so, yes...
    (as long as the manufacturers installation instructions allow it also)
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Feb 12, 2013, 11:46 AM
    Why replace the wire at all? You are replace in a 240V heater with a 240V heater. Right?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Feb 12, 2013, 12:04 PM
    Just leave it as installed, never hurts to have a bigger wire. Not sure about the
    " 300" wire, all of mine is 600Volts.
    smearcase's Avatar
    smearcase Posts: 2,392, Reputation: 316
    Ultra Member
     
    #5

    Feb 12, 2013, 12:27 PM
    Maybe I am missing something. Sounds like kshoag's plan is to put 12-3 on a 30 amp breaker?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Answers to electrical questions [ 2 Answers ]

What size schedule 40 conduit should I use to run three circuits through? (two 20amp circuits and one 15amp circuit.) The distance is 75'. About 60' is to be a surface run and the remainder will underground. I just don't want to have run three separate conduits. Thank you

Electrical questions answers [ 1 Answers ]

Have an electrical contactor single phase 220v. Contactor works when ingaged by hand.But if pushed by the pushbuttons then the contactor won't ingage.What is wrong with the push buttons that they won't work?

Electrical Questions Answers [ 1 Answers ]

Whole house 200amp generator with transfer switch do the neutral and ground wires for the circuits in panal box have to be separated

Electrical questions answers [ 1 Answers ]

I'm remodeling the kitchen and putting in new appliances . Im putting a 220 line in for a double oven where the refrigerator once was. The outlet where the oven is going is a 4 x 4 box with 1/2" EMT from the breaker box. Two questions: 1. Will 1/2 " EMT accomidate two 8 gauge hot wires...

Answers to questions on electrical [ 2 Answers ]

I have a 12 volt battery on a boat with a lot hooked to it ,the question is can I use a pos bus bar for the pos stuff and a negative bus bar for the negative stuffwithout doing any harminstead of having many wires hooked at the battery I'll have one pos and one negative.


View more questions Search