New Member
|
|
Jan 18, 2013, 06:14 PM
|
|
400 amp residential electric service
I am installing a 400 amp service on my property in Portland, Or. I will be using a double 200 amp meter base with 200 amp breaker disconnects. Just to clarify, this is a panel that has two separate 200 amp meter bases. I will be running one of the 200 amp legs to a 200 amp service panel in the house, within 10' of the meter bases. From the 200 amp service panel I will be supplying a 100 amp sub-panel in the utility room (about 35' run away).
1. What size wires and conduit should I use from the meter bases to the weather head?
2. What size wire should I use from the 200 amp meter/disconnect to the 200 amp service panel?
3. What size wire should I use from the 200 amp service panel to the 100 amp sub-panel? I will have a 100 amp breaker in the 200 amp panel for the supply.
4. As an alternative to the above scenario, I may instal the 200 amp service panel in the utility room, eliminating the need for the sub-panel (which is actually my existing main panel). In this scenario, what size wire should I use going from the meter/disconnect to the 200 amp service panel 35' away.
5. Also, most of the existing wiring in my house does not have ground wires. I would like to replace all the wiring, but would prefer to do it one room at a time, as we remodel, over the next year. Will the inspector expect to see everything in the panels grounded when they inspect my installation of the meter bases and service panel?
Thanks
|
|
 |
Uber Member
|
|
Jan 19, 2013, 04:11 AM
|
|
Assuming each meter has its own riser conduit, 3 - #4/0 aluminum XHHW, or if using SE cable, 4/0 Al 3 Wire SEU cable for each.
To the 200 amp panel, assuming SE cable, use #4/0 4 wire SER cable.
As long as no renovations are being done in the home, the inspector should not require any changes to the branch circuit wiring.
I have to ask, why two separate meters? Most utilities charge a monthly service charge for each meter.
They do make a 400 Amp (AKA 320 Amp) meter socket with two 200 amp breakers built in. Can save one monthly service charge.
|
|
 |
New Member
|
|
Jan 19, 2013, 12:18 PM
|
|
 Originally Posted by tkrussell
Assuming each meter has its own riser conduit, 3 - #4/0 aluminum XHHW, or if using SE cable, 4/0 Al 3 Wire SEU cable for each.
To the 200 amp panel, assuming SE cable, use #4/0 4 wire SER cable.
As long as no renovations are being done in the home, the inspector should not require any changes to the branch circuit wiring.
I have to ask, why two separate meters? Most utilities charge a monthly service charge for each meter.
They do make a 400 Amp (AKA 320 Amp) meter socket with two 200 amp breakers built in. Can save one monthly service charge.
I may be using one of the 200 amp services for a future business on my property. On the other hand, if it is going to cost me a lot more money to have a separate meter, maybe I should just go with the 400 amp socket. I remember when pricing them, they were spendy. I already have a double 200 amp meter base that I picked up cheap. Oh well. I guess I will be calling my utility company to see what the cost difference of the two services is.
If I do go with the 400 amp socket, what size conduit and wire should I use for the mast?
Thanks a lot for the help!
|
|
 |
Uber Member
|
|
Jan 21, 2013, 05:59 AM
|
|
One riser for a 400 amp meter would Need min of 3- #600 MCM Aluminum XHHW conductors in one 3 inch PVC Sch 40 conduit, or there can be two 2 inch PVC conduit risers each with a set of 3- #300 MCM Al XHHW conductors.
Since you already have two meter sockets, with plans for two separate metered services, you can stay with your plan.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Converting from 200 Amp to 400 Amp service-Need some advice
[ 0 Answers ]
Currently have 200 amp meter, 200 amp breaker disconnect (main service panel), and a 200 amp subpanel in a Manufactured home. I want to upgrate to 400 amp meter to service the home and a new shop with 200 amp. I have talked with the utility and local electrician and electrican engineers, but I...
Relocating and upgrading my 200 amp service to 400 amp service
[ 4 Answers ]
Im getting ready to upgrade and relocate my 200 amp service to a 400 amp service about 10 feet away away from original location. A new 400 amp meter base will be back to back with 2 new 200 amp panels. My question is, can I take out the guts out of my 200 amp panel and use it as a junction box to...
400 amp service, 2 200 amp panels, 320 amp meter socket
[ 10 Answers ]
Hi, this is my first post here, but I have been reading a lot and have already learned a bunch.
I want to thank TK already and hope you reply to this.
I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro.
I am...
400 amp service with 2-200 amp panels & 320 amp socket
[ 6 Answers ]
Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...
View more questions
Search
|