    Old Carrier furnace not heating. 120v and 24v are present and flame rollout is good.
    I have an old Carrier furnace that stopped heating. Thermostat display the time and "AC". 120v and 24v are present on the control board at the furnace. The blower works. I am getting a Service Code 33 on the LED, so I checked the Flame Rollout switch and it seems to be working (ohm meter reads "closed" across the switch). We had a power outage a few nights ago in our area and wondering if this is related. What do I check next? Is there a capacitor for starting the furnace that I should check? Any ideas out there? Thanks.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Dec 1, 2012, 02:21 PM
    Word for word, what does the diagnostics chart say for a code 33?
    bendb22's Avatar
    bendb22 Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 3, 2012, 06:06 PM
    Hi mygirlsdad77,

    Here is the error code as listed in the Carrier manual. FYI, we had a large power outage last Wednesday night and I noticed the furnace wasn't working on Thursday morning. I have 120v and 24v being supplied. I also checked the Flame Rollout Switch and that is working as it is supposed to. Thoughts? Thanks for your time on this.

    Error Code 33 - LIMIT OR FLAME ROLL-OUT SWITCH IS OPEN - If open longer than three
    Minutes, code changes to #13. Flame roll-out switch requires manual reset.
    Check for: - Defective blower motor or capacitor.
    - Dirty filter or restricted duct system.
    - Loose blower wheel.
    - Defective switch or connections.
    - Inadequate combustion air supply (Flame Roll-out Switch or fuse link open).
    - Open Flame Roll-out Switch, or fuse link. Manual reset or replace.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Dec 4, 2012, 04:32 PM
    Is this an upflow unit? If so, many time if the furnace is running when the power goes out, the residual heat will trip the auxiliary limit (this limit usually has to be manually reset just like a flame rollout) wich should be located on or near the blower wheel housing. It will be a small switch with two wires going to it and have a small button between the two wire terminals that can be pushed in to reset. Let me know what you find.

    Since the code 33 says LIMIT, OR Flame roll-out, and the flame roll-outs check good, Im betting on the limit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Carrier furnace flame rollout switch? [ 2 Answers ]

I have the 58MCA080 carrier furnace. I have the same #33 error code " Limit or Flame switch is Open". I have Flame but no air blowing, the blower is not spinning. I called a furncae guy and he told me since the blower was NOT operating the blower motor is probably bad. He believed the burner...

Carrier 58DHC075 furnace ignites but flame goes out [ 2 Answers ]

I have a Carrier natural gas furnace. Model 58DHC075-HC I think it is 92000 BTU. It was made aroung 1990 The furnace ignites OK, but then after a few seconds the flame foes out. I guess this might be due to a faulty flame detector. Is there any way I can be sure of thuis befoire I order a...

Carrier furnace flame (only) cycling [ 11 Answers ]

I have a Carrier 58GS furnace. It appears to be operating fine until I stood next to it. The gas flame comes on and off about every 5 seconds. This is not to be confused with short cycling. The blower is running as it should be and at the appropriate times. Thought before I dug into it, the...

Brayant 80t furnace, 'Limit or flame rollout switch is open"? [ 1 Answers ]

HI, I am new here and am having a furnace problem. As a new homeowner I would like to take a look at this myself before just grabbing the phone books. I have a Bryant 80t furnace. Built in 2000 and has been serviced every other year. Unit is clean and in good shape. Woke up to a cold house and...


View more questions Search