Ask Experts Questions for FREE Help !
Ask
    KDP74's Avatar
    KDP74 Posts: 8, Reputation: 1
    New Member
     
    #1

    Nov 16, 2012, 09:57 AM
    Earth and voltage generator problems
    Just bought a second hand diesel generator and connected it up to consumer unit powering sockets and lights in some stables. Maximum voltage output is showing160 volts and showing no earth even though the generator is earthed to an earth electrode. What's the problem?!
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Nov 16, 2012, 11:03 AM
    Can you give us a little more info...
    What size is the genset? (kW?)
    What kind of electrode is connected? Ground rod?
    Are the neutral and ground points on the generator connected
    Together or are they separated.
    How much load in kilowatts is connected and operating?
    KDP74's Avatar
    KDP74 Posts: 8, Reputation: 1
    New Member
     
    #3

    Nov 16, 2012, 11:17 AM
    Quote Originally Posted by hfcarson View Post
    Can you give us a little more info...
    What size is the genset? (kW?)
    What kind of electrode is connected? Ground rod?
    Are the neutral and ground points on the generator connected
    together or are they separated.
    How much load in kilowatts is connected and operating?
    Generator is 3 kw and loading is about 2.4kw. Earth rod is connected to earth terminal on front of generator. As for the neutral and ground points being connected on generator I'm afraid I don't know. Could this be my problem?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #4

    Nov 16, 2012, 11:32 AM
    Does this structure have a utility electric service?
    KDP74's Avatar
    KDP74 Posts: 8, Reputation: 1
    New Member
     
    #5

    Nov 16, 2012, 11:58 AM
    Quote Originally Posted by hfcarson View Post
    Does this structure have a utility electric service?
    No incoming utility electric supply
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #6

    Nov 16, 2012, 12:18 PM
    So this is what's known as a separately derived system...
    What you need to accomplish is a solid connection between the
    Ground, the neutral and the grounding electrode...
    This is the same way as your utility service at the first disconnect is also
    Bonded to ground.
    Now the Voltage level concerns me, how do you know it is 160 volts?
    If this was the meter on the genset, can you confirm this with a digital multimeter?
    KDP74's Avatar
    KDP74 Posts: 8, Reputation: 1
    New Member
     
    #7

    Nov 16, 2012, 12:32 PM
    Quote Originally Posted by hfcarson View Post
    So this is what's known as a separately derived system...
    What you need to accomplish is a solid connection between the
    ground, the neutral and the grounding electrode...
    This is the same way as your utility service at the first disconnect is also
    bonded to ground.
    Now the Voltage level concerns me, how do you know it is 160 volts?
    If this was the meter on the genset, can you confirm this with a digital multimeter?
    Is that like a TNC-S supply? I borrowed an earth loop impedance meter and got a reading with that. Not entirly sure how accurate it is as I was told the meter had not been calibrated for 16 months although it was never used since its last calibration date. Meter said incorrect wiring. And when I plugged in a socket tester to a socket it said there was no earth present.
    Somebody told me to put a link in the fuse board between the neutral and earth bars. Haven't tried that yet though!
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #8

    Nov 16, 2012, 12:37 PM
    I don't know the specific wiring configuration of your genset but, yes the neutral and ground do need to be connected together...
    If you are not sure about what to do, try to Google the manufacturers installation instructions before you make any adjustments or connections you are not completely sure of...
    ***Again, how do know you have 160 Volts? Meter on the genset? Digital multimeter?
    KDP74's Avatar
    KDP74 Posts: 8, Reputation: 1
    New Member
     
    #9

    Nov 16, 2012, 12:42 PM
    Quote Originally Posted by hfcarson View Post
    I don't know the specific wiring configuration of your genset but, yes the neutral and ground do need to be connected together...
    If you are not sure about what to do, try to google the manufacturers installation instructions before you make any adjustments or connections you are not completely sure of...
    ***Again, how do know you have 160 Volts? Meter on the genset? Digital multimeter?
    I used a plug in loop impedance meter which shows your voltage before you commence with any of the tests and it showed 160 volts, but as it said incorrect wiring I thought better of going any further.
    KDP74's Avatar
    KDP74 Posts: 8, Reputation: 1
    New Member
     
    #10

    Nov 16, 2012, 12:45 PM
    Quote Originally Posted by KDP74 View Post
    I used a plug in loop impedance meter which shows your voltage before you commence with any of the tests and it showed 160 volts, but as it said incorrect wiring I thought better of going any further.
    I plugged the meter in to a socket outlet if that's any help
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #11

    Nov 16, 2012, 12:56 PM
    I would still prefer a multimeter to verify voltages to neutral and ground...
    If you are actually getting a 160Vac output then this generator may be
    Malfunctioning.
    Using a voltage meter, test from Hot to Neutral, then Hot to Ground, then Neutral to Ground.
    You should read... ~120 Vac, ~120 Vac, and 0 Vac, respectively. If you can do this, let me know what you get.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #12

    Nov 16, 2012, 12:59 PM
    You plugged it in to a socket?
    And it said what?
    KDP74's Avatar
    KDP74 Posts: 8, Reputation: 1
    New Member
     
    #13

    Nov 16, 2012, 01:21 PM
    Quote Originally Posted by hfcarson View Post
    you plugged it in to a socket?
    and it said what?
    It said P-E correct and P-N correct. But a red light was lit saying incorrect wiring, do not proceed. I'll try what you suggest with the voltmeter and see what I get.
    KDP74's Avatar
    KDP74 Posts: 8, Reputation: 1
    New Member
     
    #14

    Nov 16, 2012, 01:43 PM
    [QUOTE=KDP74;3326423]It said P-E correct and P-N correct. But a red light was lit saying incorrect wiring, do not proceed. I'll try what you suggest with the voltmeter and see what I get.[/QUOTE

    Thanks a lot for your help and I'll get back to you
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #15

    Nov 16, 2012, 01:44 PM
    Good luck!
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #16

    Nov 16, 2012, 05:11 PM
    Judging by the terminology used, I think the poster is outside of the U.S. in a country that probably uses 240/230V Mains.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Generator puts out low voltage? [ 1 Answers ]

My 7KW generator has a voltage drop to 15 volts when it gets overloaded. It normally resets itself, but this last time it didn>t. Does it need a new AVR?

Generator puts out low voltage [ 1 Answers ]

My Coleman 5000 watt generator starts easy and runs great but is only putting out 190 volts. Brushes are like new. Anyone have a suggestion?

Generator voltage output too low [ 2 Answers ]

I have this 10 month old SDMO 6KVA (3.8KW) generator (with Yanmar LE100 diesel engine) which has worked OK until recently. All of a sudden I noticed that the output voltage is nowhere near the rated 230volts. On no load it measures about 210 volts and drops to about 170-180volts when loaded to...

Generator voltage 440 [ 1 Answers ]

I have a Coleman Powermate 5000. Ran well last year in snow power outage. Pluged it in this year and lost several TV and computers. Checked all the plugs and wireing, and at last found the generator was putting out 220 on each leg of the 220, and putting out 220 on the 110 side. What's wrong?

Generator Voltage [ 2 Answers ]

HELP: I have a new Coleman 1350 generator that has 2 - 120 volt receptacles on it. The problem is that the 120 volt receptacles are putting out 240 volts. I've looked for some way to get the right wiring combination, but I don't see any way to correct. The company who made the generator is no...


View more questions Search