    I have a problem with a Hot neutral. (This line hits 4 locations with lights & outlets) When disconnecting neutral (the line in question) at the panel. It is feeding back 110! When the breaker is turned off, I have continuity in both the lines. Now I could not duplicate those results further down the line when it was all hooked up.However by tracing it back I isolated All outlets in rooms 3&4.Then checked all outlets & switches at locations 1&2. I did not have a good ground at these locations & when tested Ground to neutral I would get 30 Volts? Same with ground to line 30 Volts? But get the 110 when testing line to neutral? It sounds crazy, I know. I am stumped & any help would be appreciated greatly. .
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 16, 2012, 08:36 AM
    When disconnecting a neutral at a panel with the breaker on, you will have 120 volts coming back, since it is the return conductor for the circuit, and the circuit probably was complete with lamps or some other device using the circuit.

    30 volts ground to neutral is a problem. Need to take all connections apart from panel to rooms with problem and check all connection,s possible short between neutral and ground, etc.

    Sometimes, when the bare ground gets folded in a box, it may come in contact with a neutral screw on a receptalce. That may be the cause of the issue.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Free electrical questions answers [ 1 Answers ]

I am feeding a 50 amp subpanel and would like to down size the ground and nuetral to a #8 thhn. Can this be done?

Electrical questions and answers free [ 1 Answers ]

I have my service coming into my garage,(A 200 amp box) then a 100 amp breaker to the mobile home, then a couple more breakers in the garage. I am putting a modular home in, which has a 200 amp box in also. How should I wire them together. Thanks;

Electrical questions and answers free [ 1 Answers ]

Want to put a ecosmart 150 watt bulb in garage light outlet. 120v 42watts .700 A... 35 yr old home so light is in porcelan receptacle. Came on fine then started to sprk... do I need new wire, receptacle, breaker or all three?

Free Answers to Electrical Questions [ 3 Answers ]

Is it a code violation to use seal tight to cross an expansion joint in a parking garage instead of using expansion couplings


View more questions Search