    WELL I SEEM TO BE SOME SORT OF CHALLENGED PERSON HERE. See: End of first paragraph

    I have an air compressor that is 20 amps, and I need to be able to use it in an entirely 15 amp environment. My assumption on the compressor is that it has a constant draw of less than 15 amps, but an initial startup of more than that, resulting in the 20 amp requirement. Looking at the compressor again, it is rated at 230 VAC. Does this change anything?

    From an entirely theoretical standpoint, using some custom cording and screw-on plug ends, one could make a sort of patch from a plug on breaker A to a separate plug on breaker B (both being 15 amp) and you would have a trip power of 30 amps, because of how wiring in parallel works, right? The compressor would draw an even amount of power (more or less because of wire resistance) from both lines. If something completely strange were to happen causing a fault on one breaker, that one would trip causing the other one to trip, and that would be all as far as I can see.

    Different way of putting it. You have two batteries that both put out 15 amps and the correct voltage you need, but your device draw is 30 amps. Wiring the batteries in parallel would result in the same voltage but a source amperage of 30. (where my theory that this would work comes from)

    If I did this, would it actually work or would I just start blowing breakers? I have ample wire gauge capacity, all of my plugs are correct, and this would only be temporary wherever the compressor was (plugged in and used for 10 hours or less, unplugged all other times.)
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jul 18, 2012, 06:01 PM
    There is no way to electrically, physically or legally make this work.
    Unfortunately your battery analogy does not apply with AC circuits like this.
    VEST_ERROR's Avatar
    VEST_ERROR Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 18, 2012, 09:24 PM
    I need reasons. Telling me that it won't work doesn't help me learn, although that does answer the question definitively
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jul 19, 2012, 04:53 AM
    Sorry, you'll have to get a book or three on electrical wiring and codes, because I'm not writing one.

    What you propose will violate several codes and safety standards. These can be found in the NEC and the UL White Book.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Jul 19, 2012, 06:26 AM
    Just a couple of things. By code you are not allowed to parallel conductors under the size of 1/0.
    Parallelling would increase capacity.
    Also if you were to wire ends on cords, and 1 came unplugged, the prongs would be Live and can Hurt or Kill.
    Fires are also a concern.
    If this Motor can be wired for 120/240 volts, the current would be half at 240 volts.
    If the wiring is #12 try a 2 pole 20 amp breaker.
    What is on the Name plate? Current at 240 volts, both currents may be listed?
    Just Get your Pair of #10's and a #10 ground, If needing 30 amps? It will meet code and be safe.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jul 19, 2012, 06:55 AM
    Instead of getting into the theoretical, can you tell us exactly what you have and what the issue is?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

30 amp 240 volt breaker, 15 amp outlets [ 8 Answers ]

I recently put up framing walls in my basement and am now ready to install 7 15 amp outlets. I picked up a couple 30 amp 240 volt breakers from the hardware store. My questions are is it OK to use this size breaker for 15 amp outlets? And how many outlets can I hook up to 1 breaker? Building a bar...

Can I use a 30 amp breaker to run 20 amp outlets [ 6 Answers ]

I have a 30 amp breaker with 10awg wire. I want to connect the 10awg wire to 12awg wire to run 20 amp outlets. Is that OK or do I have to change the 30 amp breaker to a 20 amp breaker?

How many wall outlets can be put on one 20 amp breaker [ 3 Answers ]

How many wall outlets can be put on one 20A breaker?

Need to run a wire from 50 amp circuit breaker to outside outlets [ 4 Answers ]

My band is performing outside. We have several pieces of equipment that need power. However, we are about 120 feet from the power source where there is a breaker box and 1 outlet. I've been told that this is a 50 amp circuit. I need several outlets to plug in all our gear. I need to know the...


View more questions Search