    RFTWOmaha's Avatar
    RFTWOmaha Posts: 2, Reputation: 1
    New Member
     
    #1

    May 27, 2012, 05:05 AM
    Reducing 200 amp to 100 amp
    Would like to replace my 200-amp service panel with a Square-D 100-amp box, and wonder if installing the 100-amp stranded aluminum wire from my 200-amp service pole breaker to the new panel will be okay. 100-amp cable (80 feet) will be encased and buried. Other than a lightning strike or an idiot with a backhoe, I can think of nothing that would cause the 200-amp service to attempt to deliver more than 100 amps to my building.
    History: Flaky lights, dimming and flickering in my 'barn.' Decided to investigate. 200-amp Federal Pacific panel in 1200-sq foot concrete block building converted to barn by previous homeowner. Went looking for lower amp breakers because the builder had wired all his socket/light circuits to 30-amp FedPacific breakers with 12/2 wire. NO junction boxes used - bared wire connections made with electrical tape/solder on all circuits, all laid on wall top plates and ceiling joists. Found one 'junction' with SIX 12/2 wires attached, just bared, taped together, and left open in the rafters! Failed to find lower-amp FedP breakers, but I did find out that FedPacific assisted America in setting fire to many mobile homes before they went out of business. Confirmed that the unit may have come from a mobile home by finding several runs of 12/2 ALUMINUM in the building! I have stripped circuits and re-run 12/2 copper only, with 220v 10-guage copper to the single 220v unit (small air compressor on a 20amp circuit.) Installed junction boxes instead of using the 'bare-wire' technique. As the building is now a barn/shop, no stove, water heater, etc. - just lights, sockets, compressor, a 1500w wall heater and a 110-volt window air conditioner in a small 'office' room I kept intact..
    Anyone see a problem with drawing 100 amps.from a 200amp service?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 27, 2012, 05:31 AM
    OK, what is the cable/wire feeding the panel now?
    If the wire is OK why replace it, and why down grade. IMO that makes no sense.

    Services don't deliver amperage, loads pull amperage. It's not like the amperage is bottled up in the service cable looking to get out. It's just available to use.
    Amperage is only a measure of current flow.

    Typically 100A is fine to a residential shop for most uses, especially if you'll be working alone most of the time, but if you have the capability to go 200A I say definitely go for it. You'll never be upset that you have too much capacity or breaker space.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    May 27, 2012, 06:02 AM
    200 Amps is the Max rated capacity of the main breaker. It has no effect on the box running 50 amps. Look for an interchange breaker to get 20 amps. If you Google Federal
    Pacific breaker interchange you should find some. Siemans breakers interchange well to Mabel panels. They may not be UL approved but are compatible.
    RFTWOmaha's Avatar
    RFTWOmaha Posts: 2, Reputation: 1
    New Member
     
    #4

    May 27, 2012, 07:20 AM
    Stanfortyman;
    Cable is 6/2 (yep, that's 6/2 run between the pole and panel 200amp breakers.) If I pull over 30 amps, I figure my grass'll catch fire. 100amp cable will be an upgrade. Prev owner was a self-styled 'electrical expert' in the neighborhood. Since I moved in, there have been several houses burn down. Electrical fires - go figure. My question is simply whether it is safe to power the 100amp cable/service panel breaker off the power pole breaker 200amp. Effectively, I believe this makes the power pole breaker useless, but my panel would break at 100+ amps anyway. Question is whether it is a problem to run 100amp cable off the 200amp service pole. I do work alone, and will rarely use over 30amps total. The 20-place Square-D is more than I need - I'll have 8 positions open when I'm done.
    jerro's Avatar
    jerro Posts: 172, Reputation: 5
    Junior Member
     
    #5

    May 27, 2012, 08:09 AM
    If you are going to run new wire to a new 100 amp panel in your building then you should be able to change the 200amp breaker at the pole service to a 100 amp breaker. The breaker at the pole is considered to be the main disconnect so the service to the building would be 100amp max.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

Can I downgrade a 200 amp service with a 200 amp main by adding a 100 amp breaker to [ 1 Answers ]

Can I downgrade a 200 amp service to a 100 amp service by adding a 100 amp breaker to the panel

Wiring 2 Gang Meter Socket w/ 100 & 200 Amp Meters [ 10 Answers ]

Hello, Are you allowed to use a 2 gang 200 amp meter socket to feed (1) 200 AMP panel and (1) 100 AMP panel, or do all meters in same enclosure have to be the same (200 AMP)? If the above is allowed: What size wire would I need from weather head to meter socket? Would I then run...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

Running 2 100 amp breaker boxes on 200 amp meter base [ 1 Answers ]

I have 2 100 amp breaker boxes,but the meter base is 100 amp.Wanting to put 200 amp metet service with disconnect box.Can some one tell me if this is possible.and how you would connect the 2 breaker boxes to the disconnect box.Thank you


View more questions Search