    How does a 240 volt thermostat work
    I have 240 volt baseboard heaters, I would like to up grade the antique thermostats. I checked the voltage at the thermostat and the wires were each 120 volts to ground. I checked voltage between the two wires and it was 240 volts. There are two termanals on the thermostat with one of these wires connected to each, no othe wire conections. How does this work, and what do I ask for at the hardware store. Thanks for the help!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 8, 2012, 03:53 PM
    Sorry your post got missed. Still need help? If the stat only has two terminals, it is a single pole unit controlling a 240 volt circuit. It is allowed by Code, I am not a proponent of it.

    The other two wires. Line and load, must be spliced together.

    Preferably, ask for a double pole stat. My preference. If they only have single pole, then replace and connect the same as existing.


    Hope this helps.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Will a 110 volt thermostat work with a 24 volt transformer? [ 1 Answers ]

I have an outdoor wood boiler and the thermostat inside our house has gone bad. I have a 24 volt transformer. Will a 110 volt thermostat work with the 24 volt transformer? Jim

Can you operate a light fixture rated for 240 volt, on 208 volt single phase? [ 1 Answers ]

I have an old street light that has a multi tap ballast, the only markings that I can read on the wires are 240volt. My system is 3phase 208 volt and I was told that I could get a 2 pole breaker and the fixture would work. Is this the case?

Can you run a 208 volt heating panel on 240 volt electrical supply [ 1 Answers ]

I have a baseboard electric heater that is 208 volts. My power supply is 240 volts. What will happen if I try to run m y 240 volt electrical supply to my 208 volt electric baseboard heater?

Will a 208 volt 3 phase mixer work off a 240 volt 3 phase service? [ 7 Answers ]

I have 240 volt 3 phase service and I have a 208 volt 3 phase mixer. Can I hook it up to the 240 volt 3 phase service? Also I have a 208 volt 3 phase oven will it work for that as well?

240 volt wiring using a single pole RLV430 thermostat [ 8 Answers ]

Using a single pole RLV430 honeywell thermostat I need to wire a 240 volt heater. In my box I have 2 live and 2 neutral wires. The thermostat has 2 wires. http://www.homedepot.ca/wcsstore/HomeDepotCanada/images/catalog/b7867367-6c05-4c82-a97c-648044b91564.pdf


View more questions Search