    Cable sizing calculation formula
    How can I calculate the cable size for given load current? With out using any tables or charts.
    sathe1963's Avatar
    sathe1963 Posts: 97, Reputation: 4
    Junior Member
     
    #2

    Nov 19, 2010, 07:07 AM
    For aluminium cables; consider 1 ampere per square mm. of cross section. For copper cable consider 1.4 ampere per sq.mm. of cross section. But, moreover to this; depending on grouping of cables, ambient temperature, laying over the ground or under ground, no. of tiers in cables trays... derating factor to be considered.
    shylaj's Avatar
    shylaj Posts: 1, Reputation: 1
    New Member
     
    #3

    Mar 26, 2011, 12:55 AM
    How can I calculate the cable size
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #4

    Sep 9, 2011, 01:49 AM
    It is not advisable to calculate cable size for a given load under given environmental conditions. You should refer to manufacturer's tables taking into consideration all the derating factors. Earth wire size could be calculated using the formula I^2.t=K^2.S^2
    Eric Lau's Avatar
    Eric Lau Posts: 2, Reputation: 1
    New Member
     
    #5

    Apr 11, 2012, 07:37 PM
    How can I know, what is cable size in mm square from cable dia(O.D)?
    What is the formula to calculate cable size
    Eric Lau's Avatar
    Eric Lau Posts: 2, Reputation: 1
    New Member
     
    #6

    Apr 11, 2012, 07:39 PM
    Please calculate for me if I know cable dia is 8mm and 6.5mm by using calipar
    redyellowpost's Avatar
    redyellowpost Posts: 1, Reputation: 1
    New Member
     
    #7

    Jan 18, 2014, 04:02 AM
    MY DEAR FRIENDS FROM ANY WHERE SEE UNDER THE PERFECT AND SUITABLE CABLE SIZING FORMULAS:

    FOR COPPER CONDUCTOR: AREA(mm2) = 0.005 *I * L (SINGLE PHASE) WHERE: 0.005 FOR MULTIPLY FACTOR
    I = LOAD CURRENT, L = LENGTH OF CABLE IN METERS.
    AREA(mm2) = 0.002488*I*L (THREE PHASE)
    ================================================== ===========================================

    FOR ALUMINUM CONDUCTORS.:- AREA(mm2) = 0.00805*I*L ( FOR SINGLE PHASE)
    AREA(mm2) = 0.004 * I * L (FOR THREE PHASE) WHERE: I = LOAD CURRENT, L = LENGTH OF THE CONDUCTOR IN MTRS.
    ----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

    DESIGNED FORMULAS BY
    ENGR.MUHAMMAD YOUNAS KHAN
    M.Sc.Engg.MIEE(UK)
    DATE: 16/01/2014
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #8

    Jan 19, 2014, 12:20 AM
    Properties of insulation and other factors too should be taken into account in addition to cross sectional area.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Earth wire cable sizing [ 3 Answers ]

Hi , Im mike, 29 years old, I live in Mauritius. I would like to know how to size my eathing wire since my supply wire is 6 mm2. Thanks

Inverter and deep cycle battery sizing calculation [ 1 Answers ]

I have a combine load of 1400watts, I want to determine the inverter and deep cycle battery required to carry my load for the period of 10hrs a day.

For calculation formula [ 3 Answers ]

Hai I need yours one help I need now a solving formula for converting the ft/min to RPM & m/min to RPM can you help me..?.

Calculation or formula [ 2 Answers ]

How to calculate the average cost per share of common stock?

Shower cable sizing [ 1 Answers ]

If I have a steam room shower, that is run off water, but I need an electric cable to feed the steamer and the light inside, the shower is 3KW and in an en suite bathroom. What size cable and what size fuse would I need??


View more questions Search