    Cable sizing calculation formula
    How can I calculate the cable size for given load current? With out using any tables or charts.
  • Nov 19, 2010, 07:07 AM
    sathe1963
    For aluminium cables; consider 1 ampere per square mm. of cross section. For copper cable consider 1.4 ampere per sq.mm. of cross section. But, moreover to this; depending on grouping of cables, ambient temperature, laying over the ground or under ground, no. of tiers in cables trays... derating factor to be considered.
  • Mar 26, 2011, 12:55 AM
    shylaj
    How can I calculate the cable size
  • Sep 9, 2011, 01:49 AM
    sinnadurai
    It is not advisable to calculate cable size for a given load under given environmental conditions. You should refer to manufacturer's tables taking into consideration all the derating factors. Earth wire size could be calculated using the formula I^2.t=K^2.S^2
  • Apr 11, 2012, 07:37 PM
    Eric Lau
    How can I know, what is cable size in mm square from cable dia(O.D)?
    What is the formula to calculate cable size
  • Apr 11, 2012, 07:39 PM
    Eric Lau
    Please calculate for me if I know cable dia is 8mm and 6.5mm by using calipar
  • Jan 18, 2014, 04:02 AM
    redyellowpost
    MY DEAR FRIENDS FROM ANY WHERE SEE UNDER THE PERFECT AND SUITABLE CABLE SIZING FORMULAS:

    FOR COPPER CONDUCTOR: AREA(mm2) = 0.005 *I * L (SINGLE PHASE) WHERE: 0.005 FOR MULTIPLY FACTOR
    I = LOAD CURRENT, L = LENGTH OF CABLE IN METERS.
    AREA(mm2) = 0.002488*I*L (THREE PHASE)
    ================================================== ===========================================

    FOR ALUMINUM CONDUCTORS.:- AREA(mm2) = 0.00805*I*L ( FOR SINGLE PHASE)
    AREA(mm2) = 0.004 * I * L (FOR THREE PHASE) WHERE: I = LOAD CURRENT, L = LENGTH OF THE CONDUCTOR IN MTRS.
    ----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

    DESIGNED FORMULAS BY
    ENGR.MUHAMMAD YOUNAS KHAN
    M.Sc.Engg.MIEE(UK)
    DATE: 16/01/2014
  • Jan 19, 2014, 12:20 AM
    sinnadurai
    Properties of insulation and other factors too should be taken into account in addition to cross sectional area.