    How to get a ground to ungrounded outlets
    I bought an older house and some of the wiring does not have the ground wire.
    Since the white wire goes to the ground in the breaker box,can I just use it to carry the ground also? Will this be safe?
    I have done some of the plug-ins with a jumper wire to the ground and white wire,have I gotten this wrong?
    Thanks for any good advice on this.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Mar 21, 2012, 08:43 PM
    Yes, you got it dangerously wrong. This is not an acceptable or safe practice.
    Grounds must not touch neutrals outside the main panel or disconnect.
    It is late so hopefully someone else will be along to expand on this.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Mar 22, 2012, 04:16 AM
    You need to remove all of those jumpers. That practice is very wrong, not allowed, and can cause serious issues.

    Replacing two wire receptacles with three wire can only be done if certain conditions are in place:

    1. Protect the entire receptacle circuit with a GFI circuit breaker, and label each 3 wire receptacle with " No Equipment Ground".

    2. Use GFI receptacles at each new receptacle and label with " No Equipment Ground".

    3. Use one GFI receptacle at the beginning of the circuit to protect the remaining receptacles in that circuit and label each 3 wire receptacle with " No Equipment Ground".

    All of the above will provide for ground fault protection but there is no equipment ground, users need to be aware of, as some equipment, such as surge protectors will not operate properly with no equipment ground.

    4. Run new cable to each receptacle that contains an equipment grounding conductor.

    There is an allowance that involves running just an equipment grounding conductor to each receptacle and grounding back at the service.

    My position is if a grounding conductor can be installed, then new cable can be installed.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #4

    Mar 22, 2012, 04:35 AM
    As Stan has said, connecting the neutrals and grounds together anywhere passed the main service disconnect can create dangerous conditions... The Electrical Codes go to great length to forbid this and only allow few exceptions.

    You say you have an older house, so likely you have two conductor cable (with a black like asphalt jacket or knob and tube), some solutions to this situation can be found in the National Electrical Code 2008 in article 406.3(D)(3)... you can use "two prong" receptacles like you probably already have or if you wish to install three-prong receptacles you have the option of installing a GFCI (ground fault circuit interrupter) to replace the two-prong receptacle. If you do, you must mark the GFCI receptacle "No Equipment Ground".

    If the GFCI is installed at the beginning of a circuit with multiple outlets you may now replace the two-prong outlets downstream with three-prong outlets as long as you mark them, "GFCI Protected" and "No Equipment Ground". This is the method that makes the most sense in my opinion from a cost perspective.

    Please be careful this is done properly... getting a permit and review by your electrical inspector will affirm you've done this correctly.
    rancher2244's Avatar
    rancher2244 Posts: 14, Reputation: 1
    New Member
     
    #5

    Mar 22, 2012, 07:32 AM
    I do want to thank each of you for your answers on this.It looks like the ground fault protectors or the way for me to go on this. Thanks again

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How can I ground a single, ungrounded 2-prong outlet? [ 9 Answers ]

We just moved into a house with a circuit in the living room that's ungrounded, and wired with 2-prong outlets. We want to set up our media center in the living room, which will require grounded 3-prong outlets. I briefly entertained the idea of installing an ungrounded GFCI 3-prong outlet,...

Older home with original wiring has three prong ungrounded outlets [ 11 Answers ]

My client is in contract to buy an Older home (1962) AS IS. The home has some lovely updates however the wiring is original. The seller replaeced all the plugs with three prong outlets that are ungrounded. Are these plugs safe? How difficult is it to ground the plugs? What type of cost is...

Outlets showing open ground [ 6 Answers ]

Hello, I started having an issue last night with my electric. All of the sudden my computers ups started beeping like crazy and I noticed it also showed an electrical fault. I tested the outlet with a 3 pronged tester and it showed an open ground. I also found 7 more outlets in the...

Adding Ground to New Outlets [ 2 Answers ]

Hi, I'm replacing the old 2 slot outlets in my house with grounded 3 prong outlets. #1: I believe the house is grounded because there is a copper rod driven into the ground adjacent to the circuit panel. Correct? #2: The receptacles with the 2 slot outlets have 4 wires (2 white, and 2...

No ground in a few outlets [ 5 Answers ]

I've searched for an answer to my question(s) and gained some insight, but still need some help. 19th century house. A lot of BX with 2-prong outlets and about half electric late installation with plastic wire with ground cable. Main panel (circuit breakers) has ground rod, but to make it more...


View more questions Search