Older home with original wiring has three prong ungrounded outlets
My client is in contract to buy an Older home (1962) AS IS. The home has some lovely updates however the wiring is original. The seller replaeced all the plugs with three prong outlets that are ungrounded. Are these plugs safe? How difficult is it to ground the plugs? What type of cost is involved?
|
|
 |
Home Repair & Remodeling Expert
|
|
Sep 17, 2009, 08:12 AM
|
|
Not safe, againist code and should be changed. If there is no ground wire present you are in a tough spot. A 3rd wire is needed and do not even think of trying to use the conduit if that is present. Can't pull a 3rd wire, then install GFCI receptacles and label not grounded. They still won't be grounded but you are safer and within code.
|
|
 |
Uber Member
|
|
Sep 17, 2009, 10:21 AM
|
|
GFCI breakers can also be used.
Did someone actually inspect the outlet and or fuse boc to make sure that 3 conductor wire isn't present.
Rewiring can be a significant expense.
|
|
 |
Home Repair & Remodeling Expert
|
|
Sep 17, 2009, 11:01 AM
|
|
The GFCI breaker would establish a GF circuit but it is not allowed to have a 3 prong receptacle with no 3rd wire attached, it would be deceptive, just like what he has now. The current owner(s) have created a situation which could be deceptive to prospective buyers who don't know about electrical systems.
|
|
 |
Uber Member
|
|
Sep 17, 2009, 11:34 AM
|
|
Mike Holt's forum discusses it here: ungrounded romex [Archive] - Mike Holt's Forum. They even suggested the change incorporated into the 2008 revision, possibly before.
I just checked the 2008 revision of the NEC, section 406.3. It does allow grounded receptacles connected to a GFCI as long as they are labeled "No Equipment Ground" and "GFCI protected".
|
|
 |
Home Repair & Remodeling Expert
|
|
Sep 17, 2009, 12:09 PM
|
|
I did not assume you meant to label the receptacle. I was only responding to exactly what you mentioned in post #3. Labeling a GFCI as ungrounded would be acceptable and not deceptive.
|
|
 |
Uber Member
|
|
Sep 17, 2009, 12:26 PM
|
|
And labeling a normal three prong ungrounded receptical downstream from a GFCI outlet or protected by a GFCI breaker must be labeled:
"No Equipment Ground" and "GFCI protected" is also permitted.
The GFCI would also need to be labeled "NO Equipment ground"
Sorry for all the confusion.
I was reading your post as every outlet must be replaced with a GFCI receptacle which is not true. Three prong ungrounded receptacles must be properly labeled and protected by a GFCI somewhere.
|
|
 |
Home Repair & Remodeling Expert
|
|
Sep 17, 2009, 01:20 PM
|
|
We are on the same page, just got there via different routes
|
|
 |
Home Improvement & Construction Expert
|
|
Sep 17, 2009, 01:23 PM
|
|
KISS,
Any suggestions for finding the 1978 NEC code?
|
|
 |
Uber Member
|
|
Sep 17, 2009, 01:32 PM
|
|
|
|
 |
Home Improvement & Construction Expert
|
|
Sep 17, 2009, 01:42 PM
|
|
Don't want to buy it, just check it. My memory says that some time in the past the accepted method of replacing ungrounded outlets with grounded outlets was to pigtail the ground to the neutral. That was of course before the advent of GFIs. That is just my memory and cannot necessary be trusted and I don't want to say it. If my memory is accurate, the correct response to this post would be "It depends on when the grounded outlets were installed."
|
|
 |
Full Member
|
|
Sep 18, 2009, 05:54 AM
|
|
There is another option here. Not as good as have a continuous ground. I have seen this situation before, and it is deceptive.
Check to see if the wiring in the house has metal boxes and armored cable that runs to the panel. (not broken) The alternative then, would be to ground each receptacle with a pigtail screwed to the box. In a 1960 house, metal boxes and armoured cable is common.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
What is the best way to change 2 prong outlets to Three prong outlets?
[ 7 Answers ]
Gentlemen, Im getting a bit of mixed info on this subject and am looking for some help. I have an old house (1950's) with 2 prong outlets and They were wired with old 2 wire rag wire with no ground. The house is on slab and has vaulted ceilings throughout with no attic access. I believe I have a...
Home built in 1952 with ungrounded wiring What can I do?
[ 3 Answers ]
Okay I have been reading as much as possible about home electrical wiring and plan to pick up a book from the library and read some more. However I am novice when it comes to electrical am I crazy for thinking I can do these repairs on my own with a little reading (I am a pretty quick study). I...
Two wire ungrounded systen in older homes
[ 1 Answers ]
Hi , wife and I live in her mothers house now, it is a two wire ungrounded system throughout. She had someone come in and wire it with grounds, not everything had grounds but half of it did after he was done rewiring it, but the city inspector came through to look at it and said it was a fire...
Adding outlets to older (50's) home
[ 1 Answers ]
Supposing no upgrades need to occur with my homes main panel, what is a fair appraisal of how much it would cost to add a 220 outlet and breaker for a dryer and a few 120 outlets for a home office? Attic and basement are open and unfinished, so access shouldn't be too much of an issue.
Also, if I...
Converting 2-prong outlets to 3-prong
[ 1 Answers ]
I live in an old house were only a few of the outlets are 3-prongs. I want to change all the existing 2-prong outlets (as buying cheaters is annoying) to some GFCI outlets, but I have a problem.
There are no light fixtures in the house, and all the light switches run the top slot on the outlets,...