    Installing 100 amp breaker in 200 amp panel
    I had a mobile home and lot given to me. The mobile home has a fairly new 200 amp inside panel box with 100 amp service coming in from the power pole. It also appears on this Siemens 200 amp panel box that the 200 amp breaker is attached to the panel box. Could I snap in a 100 amp breaker on the power bar in the 200 amp box and run the service wire (from the outside power pole) to the 100 amp breaker and use the 100 amp breaker as the main breaker? Would this work if the 200 amp breaker remained in the box and I switched the 200 amp breaker to "off?" I hate to replace the box as I may be upgrading in the future.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Mar 16, 2012, 03:43 AM
    Assuming that you mean that you have a panel with a 200 amp main breaker inside and also assuming that you have a 100 amp breaker on the pole, just use the 200 amp you have. The 100 amp outside will serve as your over load protection and the 200 amp inside will serve as a disconnect.only. Not need to change anything. Cable from pole to inside will have to be sized to fit breaker on pole anyway.
    kehutto's Avatar
    kehutto Posts: 2, Reputation: 1
    New Member
     
    #3

    Mar 16, 2012, 07:09 PM
    Thanks.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

Can I downgrade a 200 amp service with a 200 amp main by adding a 100 amp breaker to [ 1 Answers ]

Can I downgrade a 200 amp service to a 100 amp service by adding a 100 amp breaker to the panel

Main Cutoffs: 200 amp outside panel feeding a 200 amp inside circuit breaker panel. [ 1 Answers ]

Would you please clarify an answer you gave to a previous question? Your answer makes me wonder about the capacity of the main shut-off circuit breaker in an inside circuit breaker panel. Is the inside circuit breaker panel the same as what you call a subpanel? Here's the question and answer:...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...


View more questions Search