    Can and should 12/3 romwx be used to supply 2 circuits?
    The red wire would be connected to a separate breaker
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Mar 7, 2012, 09:12 PM
    Yes, called two circuits sharing a neutral, code requires a double breaker be used.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Mar 8, 2012, 03:36 AM
    While a shared neutral is allowed, all connections of the white neutral must be spliced, connecting on terminals on devices such as receptacles is not allowed. An open neutral of a multiwire circuit can be damaging to the appliances on the circuit.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Mar 8, 2012, 09:47 AM
    Suggested editorial change "Spliced" to "Pigtailed"

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Clog in water supply lines after replacing section at main municipal supply... [ 1 Answers ]

I had an exposed water supply line that ran from the city inlet to my house. It was old and rusty so we decided to replace it with a PEX pvc piping. It's the same dia. (3/4") and we replace the one 90 elbow with a 45 instead. When we turned the water back on, it had no pressure, and after my...

I need 110 vac for my circuit. But main supply gives 220 vac supply. [ 0 Answers ]

I belong east side country not west. So how can I split my main supply into two 110vac supply for my circuit. I will thankful.

Supply line won't stop running. Main water supply off [ 3 Answers ]

I was doing some bathroom remodeling and attempted to remove an old supply valve. It would not budge so I decided to cut the copper tubing underneath it and put on a new shutoff valve with a compression fitting. The problem is that water just kept coming out of that supply line. The main water...

3 phase supply Vs 1Phase Supply [ 1 Answers ]

I wanted to know difference between 3 phase and 1 phase conceptually

Changed out radiator w/copper supply baseboard w/ pex supply [ 2 Answers ]

And there is no heat in eminating from this baseboard. This was done in one room only and off the original radiator line.the system is all hotwater radiator w/the exception of this one room. We did not change the original heating supply line to this but added valves and then the pex. Seems the hot...


View more questions Search